    Sizing of Capacitor bank



    Dear all,

    Can someone advise how do we size a capacitor bank for power factor regulation. Approx 0.95

    Assuming a supermarket with
    4 x 18 kW low temp compressor
    4 x 30 kW mid temp compressor

    10 x 3.75 m double well island freezer
    7 x vertical open freezer
    15 x 3.75 dairy multideck
    8 chiller room
    7 freezer room

    Main DB is sized at 500 amp to cater for starting high amp.

    Wat is the required KVAR and how many steps should I use?

    Thanks,
    Kevin



  2. #2
    Join Date
    Jan 2005
    Location
    Norfolk, U.K
    Age
    44
    Posts
    65
    Rep Power
    20

    Re: Sizing of Capacitor bank

    I think this is quite a specialist subject.

    I have recently had new power factor correction equipment installed on my site, (a large cold storage and distribution site). i have a large panel which covers the whole electrical installation on site, the power factor correction is fully automatic and has a controller to bring in & out the capacitor banks (4 in total) as and when required depending on what plant or equipment we are running at the time, we now have a power factor of around 0.98 all the time. I used a company called ABB, it might be worth looking at thier website.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Sizing of Capacitor bank

    Hi Kevin,

    I agree with ecclesk on this one.
    You will need an electrical design engineer to design the panel and the controller.

    ABB is a fine company but every manufacturer can supply you the equipment.

    Make sure that whatever is offered you, replacement parts supply, is not too far.

    Chemi

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Sizing of Capacitor bank

    It's very difficult to predict with the figures you gave.
    It depends on the lights in the cabinets used (perhaps already a CAP mounted in it), type of compresser used, is the compresser running in part load or full load, number and type of fans used in the cabinets, fans of the condenser, ...

    See for more help http://www.bchydro.com/rx_files/psbu...siness1531.pdf
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jul 2005
    Location
    Malaysia
    Age
    44
    Posts
    66
    Rep Power
    19

    Re: Sizing of Capacitor bank

    Guys,

    I've summed up all power consumption for compressors, showcase heaters, lighting and fan to obtain apparent power.

    Then to check uncorrected power consumption for each equipment, compressors and so on. Say 0.7

    Required KVAR can be obtained [ desired power factor 0.92) by using

    Req Kvar = ((tan(inv cos 0.7)-tan(inv cos 0.92))

    Till now i have been able to maintain the power factor without problem..

    Thanks for the input..

    Rgds,
    Kevin
    Attached Files Attached Files

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Sizing of Capacitor bank

    Hi Kevin

    Sorry missed this post. Your are assuming a 0.7 power factor, however it may vary.

    The only point I would make is error on the side of caution, make it too big, the controller on the PF Bank will stage it in anyway, using only the banks that are required.

    Kind Regards Andy.

  7. #7
    Join Date
    Mar 2006
    Location
    Qto - Ec.
    Age
    60
    Posts
    5
    Rep Power
    0

    Re: Sizing of Capacitor bank

    Could you let me know what is the nominal power factor in the name plate of the equipment.
    So I could help you.
    Additionally, You could have two types just one step or automatic two o more steps

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Sizing of Capacitor bank

    Be careful of PWS starting compressors with capacitors. They are causing leading currents and stators loss of insulation when starting.

  9. #9
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Sizing of Capacitor bank

    Years ago, Copeland Application Bulletins discussed power factor correction with capacitors and had reservations about it for small compressors, part winding starts (as NoNick mentioned) and certain other applications. It may or may not be relevant, but I will see if I can find it.

    Go to https://www.emersonclimatecustomer.c...et/CTP02_LogIn

    Click on "Product information" After you register you can log in and look for online product information. You want application engineering bulletin No. 1249. If that doesn't work, just try starting at an earlier page and get to the Copeland brand and register. http://www.gotoemerson.com/jsp/brand...tech/index.jsp

    At least they have some good calculation guidelines in how to do it properly. I could also email you the pdf file if you would prefer.

  10. #10
    ahmed251's Avatar
    ahmed251 Guest

    Re: Sizing of Capacitor bank

    Quote Originally Posted by Kevin Yeo View Post
    Guys,

    I've summed up all power consumption for compressors, showcase heaters, lighting and fan to obtain apparent power.

    Then to check uncorrected power consumption for each equipment, compressors and so on. Say 0.7

    Required KVAR can be obtained [ desired power factor 0.92) by using

    Req Kvar = ((tan(inv cos 0.7)-tan(inv cos 0.92))

    Till now i have been able to maintain the power factor without problem..

    Thanks for the input..

    Rgds,
    Kevin
    Hello Mr. Kevin
    How r u?
    We have project and we are using 45KVAR capacitor bank in this project for MCC panel. Now my client is asking for calculation. my total load is 96.3KW.
    Actual power factor is 0.8 and targeted PF is 0.95 at 415V, 50HZ. But i am not getting 45KVAR please send me any solution for this.
    Request please

Similar Threads

  1. Piping and line sizing in lbs/min
    By Kathleen in forum Tools and Calculators
    Replies: 18
    Last Post: 29-05-2009, 03:07 PM
  2. Compressor sizing using R404a
    By PCL in forum Refrigerants
    Replies: 4
    Last Post: 14-08-2006, 11:09 PM
  3. Sizing for Australia
    By dogma in forum Fundamentals
    Replies: 5
    Last Post: 17-03-2006, 10:05 AM
  4. 134a surge drum sizing
    By Camille in forum Refrigerants
    Replies: 0
    Last Post: 03-03-2006, 01:44 PM
  5. expansion water tank sizing program
    By Lc_shi in forum Fundamentals
    Replies: 0
    Last Post: 01-09-2005, 04:24 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •