Results 1 to 10 of 10
Thread: Sizing of Capacitor bank
21-10-2005, 06:26 AM #1
Dear all,
Can someone advise how do we size a capacitor bank for power factor regulation. Approx 0.95
Assuming a supermarket with
4 x 18 kW low temp compressor
4 x 30 kW mid temp compressor
10 x 3.75 m double well island freezer
7 x vertical open freezer
15 x 3.75 dairy multideck
8 chiller room
7 freezer room
Main DB is sized at 500 amp to cater for starting high amp.
Wat is the required KVAR and how many steps should I use?
Thanks,
Kevin
21-10-2005, 10:13 AM #2
Re: Sizing of Capacitor bank
I think this is quite a specialist subject.
I have recently had new power factor correction equipment installed on my site, (a large cold storage and distribution site). i have a large panel which covers the whole electrical installation on site, the power factor correction is fully automatic and has a controller to bring in & out the capacitor banks (4 in total) as and when required depending on what plant or equipment we are running at the time, we now have a power factor of around 0.98 all the time. I used a company called ABB, it might be worth looking at thier website.
21-10-2005, 01:16 PM #3
Hi Kevin,
I agree with ecclesk on this one.
You will need an electrical design engineer to design the panel and the controller.
ABB is a fine company but every manufacturer can supply you the equipment.
Make sure that whatever is offered you, replacement parts supply, is not too far.
Chemi
21-10-2005, 09:49 PM #4
It's very difficult to predict with the figures you gave.
It depends on the lights in the cabinets used (perhaps already a CAP mounted in it), type of compresser used, is the compresser running in part load or full load, number and type of fans used in the cabinets, fans of the condenser, ...
See for more help http://www.bchydro.com/rx_files/psbu...siness1531.pdfIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
08-03-2006, 06:01 AM #5
Guys,
I've summed up all power consumption for compressors, showcase heaters, lighting and fan to obtain apparent power.
Then to check uncorrected power consumption for each equipment, compressors and so on. Say 0.7
Required KVAR can be obtained [ desired power factor 0.92) by using
Req Kvar = ((tan(inv cos 0.7)-tan(inv cos 0.92))
Till now i have been able to maintain the power factor without problem..
Thanks for the input..
Rgds,
Kevin
31-03-2006, 10:33 PM #6
Hi Kevin
Sorry missed this post. Your are assuming a 0.7 power factor, however it may vary.
The only point I would make is error on the side of caution, make it too big, the controller on the PF Bank will stage it in anyway, using only the banks that are required.
Kind Regards Andy.
04-04-2006, 08:03 PM #7
Could you let me know what is the nominal power factor in the name plate of the equipment.
So I could help you.
Additionally, You could have two types just one step or automatic two o more steps
04-04-2006, 10:45 PM #8
Be careful of PWS starting compressors with capacitors. They are causing leading currents and stators loss of insulation when starting.
07-04-2006, 12:56 AM #9
Years ago, Copeland Application Bulletins discussed power factor correction with capacitors and had reservations about it for small compressors, part winding starts (as NoNick mentioned) and certain other applications. It may or may not be relevant, but I will see if I can find it.
Go to https://www.emersonclimatecustomer.c...et/CTP02_LogIn
Click on "Product information" After you register you can log in and look for online product information. You want application engineering bulletin No. 1249. If that doesn't work, just try starting at an earlier page and get to the Copeland brand and register. http://www.gotoemerson.com/jsp/brand...tech/index.jsp
At least they have some good calculation guidelines in how to do it properly. I could also email you the pdf file if you would prefer.
28-03-2009, 06:08 AM #10
Hello Mr. Kevin
How r u?
We have project and we are using 45KVAR capacitor bank in this project for MCC panel. Now my client is asking for calculation. my total load is 96.3KW.
Actual power factor is 0.8 and targeted PF is 0.95 at 415V, 50HZ. But i am not getting 45KVAR please send me any solution for this.
Request please
Piping and line sizing in lbs/min
By Kathleen in forum Tools and CalculatorsReplies: 18Last Post: 29-05-2009, 03:07 PM -
Compressor sizing using R404a
By PCL in forum RefrigerantsReplies: 4Last Post: 14-08-2006, 11:09 PM -
Sizing for Australia
By dogma in forum FundamentalsReplies: 5Last Post: 17-03-2006, 10:05 AM -
134a surge drum sizing
By Camille in forum RefrigerantsReplies: 0Last Post: 03-03-2006, 01:44 PM -
expansion water tank sizing program
By Lc_shi in forum FundamentalsReplies: 0Last Post: 01-09-2005, 04:24 AM