    Panasonic Split cassette- Compressor Tripping



    Hey guys, Got another doosey. I just want to double check my finidings with some experienced techs.

    I have a 10 kw panasonic split casset unit, At arrival i found the unit in what the fault code said to be compressor o/l protection. I reset unit and compressor would start up and seem fine, but within 15-20 seconds it would start to make a loud/rattle noise and trip. The system would do this 4-5 times then the pcb would obviously show up the same fault (compressor o/l)

    I measured the current and when compressor sounded normal it was pulling around 15-17amps, but at about 15-20 seconds run time you could here it load up, get noise and increase amps close to 30amps and then trip.

    Starting for the compressor is permanent split capacitor. I was thinking possibly the caps are ****ged. I visually inspected them, They seemed o.k but did not test them as i didnt have a capacitance tester with me.

    In my opinion the compressor seems to be mechanically locking up due to the sound therefore pulling over amps, but im also wondering why it sounds normal and pumps for the 15-20 seconds before the noise and trip happens.

    The manager on site said a few days prior to me being on site that the outdoor unit was making a loud noise. ( i think this was the start of the comp failing)

    Any thoughts? Cheers. P.s Valves are open



  2. #2
    Join Date
    Feb 2008
    Location
    QLD
    Age
    53
    Posts
    74
    Rep Power
    17

    Re: Panasonic Split cassette- Compressor Tripping

    Outdoor unit model number, and the actual faultcode please? (F32-05) ?

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Panasonic Split cassette- Compressor Tripping

    Sounds more like flood back with the loud rattle noise

  4. #4
    Join Date
    Nov 2011
    Location
    Australia
    Posts
    4
    Rep Power
    0

    Re: Panasonic Split cassette- Compressor Tripping

    This sounds worse then flood back although it may be.

    Stefs- you have the right fault code it was f32-05 Compressor overcurrent protection.

    The model of the outdoor unit is CU-B34DBE5.

    cheers

  5. #5
    Join Date
    Feb 2008
    Location
    QLD
    Age
    53
    Posts
    74
    Rep Power
    17

    Re: Panasonic Split cassette- Compressor Tripping

    First thing I would do, is remove the soft starter (sure start6?) and return the wiring to factory, and try again.

    (but I suspect your compressor has failed)
    Last edited by stefs_cruiser; 30-11-2011 at 02:30 AM.

  6. #6
    Join Date
    Dec 2010
    Location
    ZA
    Posts
    154
    Rep Power
    16

    Re: Panasonic Split cassette- Compressor Tripping

    Change the capacitor first, before you condemn the compressor. Capacitors can fail under load, best is to try a replacement. Just to test it can be a value close to the recommended, or a little higher. 20% up or 10% down is ok for testing.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Split cassette- Compressor Tripping