    Production area cooling



    Hi folks

    I have been asked to refrigerate a game (ie meat) production area and are not to sure of what evaporator/s to specify. The required temp must be 6 to 10 degrees and the airflow must be gentle for the comfort of the staff working. additionaly the coolers must be roof mounted with side air flow, that is not blowing downwards.

    The internal height is 2.7m and the floor is 9.6m X 6.0m giving a volume of 156m/3


    Any suggestions regarding the specification and sizing would be most welcome. there will be up to 10 people working and electrical load from machinary and lighting will be in the order of 2kw.

    Many thanks



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Production area cooling

    pick a evap manufacturer and talk to them.
    They will advise.
    You have a good manufacturer in Farnham already.
    Grizzly

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Production area cooling

    Have a look at these fabric air ducts, if you can apply them, they meet the requirments you asked for.
    http://www.fabricair.com/uk/

  4. #4
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: Production area cooling

    try a dual discharge unit sits in the middle of the room and blows both ways several wholesalers do a low temp dual discharge unit with variable speed the last one we had i believe come out of heronhill

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Production area cooling

    tip,get the evap coils treated with blygold or similar fin treatment,also ensure the light fittings are weather proof, also with horizontal airflow this reduces complaints of draughts, reducing airflow decreases capacity and thus requires more defrosts-staff can wear gloves if a 6deg enviroment is not to their liking

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Production area cooling

    Done something similar with a twin fan Searle evap, had special fan gaurds that you fit a fabric sock on like the ones Chemi linked to that run the length of the room. They fit into a channel in the roof. Need a set to use and a set to wash.

    Or maybe a dual discharge cooler, depends on customers budget.