    Daikin split System cant get suction pressure out of a vaccum Help plz



    I've got a Daikin RYP100 L7V1 split wall mounted R407C system. The system has the correct weight of refrigerant. The suction pressure wont come out of a vacuum. I have tested the 4 way valve which seems ok. I changed the head of the expansion valve with another unit which was working ok and the suction pressure still pulls into a vacuum. The 4 way valve was changed recently is it possible that the heat from the valve change could have damaged the expansion valve body? Or could it be a blocked strainer? If anyone could help me please that would be great as I am stuck.



  2. #2
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: Daikin split System cant get suction pressure out of a vaccum Help plz

    have you done a flow check poss blockage ot eev shutdown/ on startup does it level up? service valve part shut/ is it on a long piperun? when shut of does pressures level up? how long does it run for remember those daikins have a pump down button

  3. #3
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Daikin split System cant get suction pressure out of a vaccum Help plz

    pull the strainer just after the expansion valve, have seen a few of these blocking up

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Daikin split System cant get suction pressure out of a vaccum Help plz

    Hi Stephen
    I recently worked on a Daikin Split (horrible things). Replaced the compressor and had low suction pressure for R22 about 40psi. Phoned tech support and they advised to chang the PCB, compressor contactor and two thirmistors. The problem was still there, considering my knowedge and experience is limited I handed the job to another more experienced tech. He removed and recharged unit by weight as I did and the same poblem is there. Now it is a six week wait for a capillary set as #3 capillary is blocked. Would have been cheaper to replace the unit. Check for frosting on capillaries and ensure indoor coil is clean.

  5. #5
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Daikin split System cant get suction pressure out of a vaccum Help plz

    just seen your from ni, is this a site in belfast?

  6. #6
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin split System cant get suction pressure out of a vaccum Help plz

    Stepen 22,
    How long did you let the unit operate? On start up these units do a type of pump down which last around 90secs.

    If the mains power is switched off then back on you should be able to feel the EV motor driving, you can also hear a ticking sound from the EV as the PCB verifies the valve is fully closed when power is switched on.
    Have you tested the unit in both heating and cooling mode? Does the internal piping show signs of overheating with welding tourch? The interal piping has 4 check valves, refrigerant flow is allowed to pass through 2 of the check valves in cooling and passes through the other 2 when operating in heating. If these check valves have been over heated the plastic iternals can melt causing a blockage.

    I would suggest you reclaim the gas charge, split the internal piping and purge OFN through the pipes to identify the location of the blockage. You can also purchase a magnet to manually open the EV for testing.
    Last edited by VRVIII; 24-11-2011 at 10:54 PM.

  7. #7
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Daikin split System cant get suction pressure out of a vaccum Help plz

    Quote Originally Posted by stephen 22 View Post
    I've got a Daikin RYP100 L7V1 split wall mounted R407C system. The system has the correct weight of refrigerant. The suction pressure wont come out of a vacuum. I have tested the 4 way valve which seems ok. I changed the head of the expansion valve with another unit which was working ok and the suction pressure still pulls into a vacuum. The 4 way valve was changed recently is it possible that the heat from the valve change could have damaged the expansion valve body? Or could it be a blocked strainer? If anyone could help me please that would be great as I am stuck.
    Check your service shut off valves before anything else.