    Danfoss EKC 331T



    Fellow Members


    Have problem with Danfoss EKC 331 T which was use as compressor
    controller which control 3 compressor on a compresor rack.On the Display reads "OFF"
    and as we do the checking the relays out on the compressor is open.We check the transducer,the cable and the wiring and it ok.

    Dont have in mind what went wrong.Please help.


    abet

  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Danfoss EKC 331T

    Abet.

    Read the first sentence under the heading of Micellaneous on the attached page.
    Someone has been finger poking.

    Grizzly

  3. #3
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Danfoss EKC 331T

    Grizzly,

    Does it mean the transducer is defective?we try the transducer to other controller and
    it works ok.Any other way sir,to solve this,if you wont mond.
    abet

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Danfoss EKC 331T

    Quote Originally Posted by abet_meneses View Post
    Grizzly,

    Does it mean the transducer is defective?we try the transducer to other controller and
    it works OK.Any other way sir,to solve this,if you wont mond.
    Abet.
    It could be, but I suspect one of the options 1 to 11 has not been selected.
    Therefore the controller does not know which option it is to control by.
    And therefore is in shutdown mode.
    Read it again and you should understand more.
    Grizzly

  5. #5
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: Danfoss EKC 331T

    If parameter o22 is set to #2 then opening the circuit between terminals 19 and 20 will cause all control to stop and display "off". This is like an external start stop and could be used in conjunction with a possible manual reset HP control to stop the controller calling for compressors on an HP trip - this is just one example of any such application, it could be used to start and stop the rack for any number of reasons.

    Full manual here
    http://www.ra.danfoss.com/TechnicalI...1/RI8GZ353.pdf
    ...and she said "give it to me you big fridgie"

  6. #6
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Danfoss EKC 331T

    Grizzly,
    In parameter o10 our setting is #3 since we have AKS 32R for compressor regulation.

    750 Valve.
    In parameter o22 our setting is #2.and yes we have open it So display is OFF.Since we already re connect it the display is now 0.01 but the relay terminal 3 & 4 is close while other two relay remain open.On parameter o20 as -1C is the setting while on o21 we set it on -12.I"m at lost why relay term.5&6 and term.7 & 8 doesnt close to operate the other two (2) compressors.
    abet