24-11-2011, 01:03 PM #1
Danfoss EKC 331T
Fellow Members
Have problem with Danfoss EKC 331 T which was use as compressor
controller which control 3 compressor on a compresor rack.On the Display reads "OFF"
and as we do the checking the relays out on the compressor is open.We check the transducer,the cable and the wiring and it ok.
Dont have in mind what went wrong.Please help.
abet
-
24-11-2011, 10:05 PM #2
Re: Danfoss EKC 331T
Abet.
Read the first sentence under the heading of Micellaneous on the attached page.
Someone has been finger poking.
Grizzly
-
24-11-2011, 10:25 PM #3
Re: Danfoss EKC 331T
Grizzly,
Does it mean the transducer is defective?we try the transducer to other controller and
it works ok.Any other way sir,to solve this,if you wont mond.abet
-
25-11-2011, 06:55 AM #4
-
25-11-2011, 07:17 AM #5
Re: Danfoss EKC 331T
If parameter o22 is set to #2 then opening the circuit between terminals 19 and 20 will cause all control to stop and display "off". This is like an external start stop and could be used in conjunction with a possible manual reset HP control to stop the controller calling for compressors on an HP trip - this is just one example of any such application, it could be used to start and stop the rack for any number of reasons.
Full manual here
http://www.ra.danfoss.com/TechnicalI...1/RI8GZ353.pdf...and she said "give it to me you big fridgie"
-
25-11-2011, 09:52 AM #6
Re: Danfoss EKC 331T
Grizzly,
In parameter o10 our setting is #3 since we have AKS 32R for compressor regulation.
750 Valve.
In parameter o22 our setting is #2.and yes we have open it So display is OFF.Since we already re connect it the display is now 0.01 but the relay terminal 3 & 4 is close while other two relay remain open.On parameter o20 as -1C is the setting while on o21 we set it on -12.I"m at lost why relay term.5&6 and term.7 & 8 doesnt close to operate the other two (2) compressors.abet