    Toshiba VRV Systems



    HI Guys
    Have any one been suffering from 5/8 flare nuts splitting on a Toshiba R410a 3 Pipe VRV system according to Toshiba they have not heard of any problems. The system is about 7 years old
    Many thanks

    [edit] Moved to the correct section.
    Last edited by Brian_UK; 23-11-2011 at 10:10 PM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Toshiba VRV Systems

    Probably incorrectly fitted or poor quality nuts in the first install.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Toshiba VRV Systems

    .



    There has always been an issue with flare nuts splitting on components that are liable to frost - hence the restriction on flares fitted to TEVs in the standards - but having said that a VRV indoor set should never frost. so, back to what Brian said.




    .

  4. #4
    Join Date
    May 2006
    Location
    Hayling Island, UK
    Age
    60
    Posts
    143
    Rep Power
    21

    Re: Toshiba VRV Systems

    I worked for Toshiba Tech Dep UK for nearly 30 years and can honestly say I've never heard a VRF R410a suffering with split flare nuts. So what they told you is correct.

    You don't say if the flare nuts are indoor or outdoor.

    I concurr with what Brian said, although I think the flare nuts Tosh use are perfectly up to scratch. They might have been over-tighten, hard to say after a failure.

    My first boss use to say the correct tightness for a nut was up to sheer and back off half a turn!!!! (He wasn't serious)

    Cheers

    Loops

  5. #5
    Join Date
    Feb 2005
    Location
    Australia
    Posts
    123
    Rep Power
    21

    Re: Toshiba VRV Systems

    Quote Originally Posted by Loops View Post
    I worked for Toshiba Tech Dep UK for nearly 30 years and can honestly say I've never heard a VRF R410a suffering with split flare nuts. So what they told you is correct.

    You don't say if the flare nuts are indoor or outdoor.

    I concurr with what Brian said, although I think the flare nuts Tosh use are perfectly up to scratch. They might have been over-tighten, hard to say after a failure.

    My first boss use to say the correct tightness for a nut was up to sheer and back off half a turn!!!! (He wasn't serious)

    Cheers

    Loops
    Actually if you have the flare that caused the cracked nut it is very easy to see how tight it was done up.
    Get a micrometer with pointed anvils and measure the thickness of the copper pipe in the flared section and compare it to the actual wall thickness of the copper pipe. The flared section of pipe crushes just like a head gasket in a car engine does when it is tightened and provides a witness to torque used.
    I am sure Toshiba will have some tables which graph deformation of the copper versus the torque of the flare nut for the various pipe sizes. I know that Fujitsu, Panasonic and Daikin have that sort of information floating around internally. You will probably find that the cracked nuts had their flares tightened more than 50% higher than the specified tension for the size flare.

    I did the experiment once on 3/8" flares making up some sample flares as per Fujitsu's R410A product installation manuals and then putting a male flared union in a bench vice and tightening up the samples using a new flare nut each time to various tensions with a torque wrench from 20 - 70 Nm in 10Nm increments. I then marked each flare and kept them handy in my office, it was amusing to compare them with samples of cracked flare nuts and flares that contractors used to send back to me as being "defective". As whenever someone tried to claim for "defective or cracked flare nuts" I would make them submit the actual flare with the defective sample or would not even consider it.

  6. #6
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    20

    Re: Toshiba VRV Systems

    I heard a while ago from 1-2 engineers that there was something about using soapy liquid to test for leaks on flare joints -- leaving it on the joint rather than washing it off afterwards -- and it would somehow crack the nut, either from combining the cold weather or just.... somehow weakening the metal.

    I guess over tightening may be a more plausible cause but anyone know more about the soapy liquid idea?

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba VRV Systems

    taken from page 22 of a tosh vrv manual• Tightening torque of flare pipe connections
    Pressure of R410A is higher than that of R22 by
    approx. 1.6 times. Therefore, using a torque wrench,
    tighten the flare pipe connecting sections which
    connect the indoor and outdoor units of the specified
    tightening torque. Incorrect connections may cause
    not only a gas leak, but also a trouble of the
    refrigerating cycle.
    REQUIREMENT
    If an excessive torque is applied, the nut
    may crack depending on the installation
    conditions.
    Airtight test/Air purge, etc.
    For airtight test, air purge, addition of refrigerant, and
    gas leak check, follow the Installation Manual attached
    to the outdoor unit.
    REQUIREMENT
    Be sure to use the tool such as charge hose
    exclusive to R410A.
    Do not turn on the power until the airtight test and
    the vacuuming have finished. (If turning on the
    power, the incorporated PMV is closed fully and
    the period until the vacuuming finishes elongates.
    Open fully valves of the outdoor unit
    Gas leak check
    Check with a leak detector or soap water whether gas
    leaks or not, from the pipe connecting section or cap
    of the valve.
    REQUIREMENT
    Use a leak detector manufactured exclusively for
    HFC refrigerant (R410A, R134a, etc.).
    Connecting pipe
    outer dia. (mm)
    Ø6.4
    Ø9.5
    Ø12.7
    Tightening torque
    (N•m)
    14 to18 (1.4 to 1.8 kgf•m)
    33 to 42 (3.3 to 4.2 kgf•m)
    50 to 62 (5.0 to 6.2 kgf•m)
    Re-tightening
    torque (N•m)
    18 (1.8 kgf•m)
    42 (4.2 kgf•m)
    62 (

  8. #8
    Join Date
    Jun 2010
    Location
    geraldton western australia
    Age
    39
    Posts
    57
    Rep Power
    14

    Re: Toshiba VRV Systems

    a good reason why everyone should use torque wrenches..

  9. #9
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Toshiba VRV Systems

    I have previously work for a Toshiba main dealer and about 6 years ago there was a serious issue with a duff batch of flare nuts across all ranges.
    The company line is always going to be "deny all accountability".
    That said a number of other manufacturers were also affected.
    Some of you who deal with Mitsubishi Electric may have noticed a few years ago they started supplying flare nuts with holes drilled just behind the flare face at 12,3,6 and 9 o clock.
    This was a direct result of the issues surrounding the duff batch.
    The idea was to allow any moisture trapped in the threads to drain out and prevent freeze splits.
    I have a few photos of these nuts I'll try find and post later.
    PS. never torqued a flare nut and not likely to start now.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  10. #10
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Toshiba VRV Systems

    had to move a early 410 mitsi wallmount the other day, the suction nut required a 18 inch long adjustable wrench and a smaller wrench with 18 inches of uni strut to get a bit more leverage , i hate to think of the size of the bloke who fitted this system. only seen a few cracked flares , but love my torque wrench

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba VRV Systems

    i didnt fit it as ive never been the jersey channel-so this monkey isnt guilty!