    McQuay strange pumpdown / LLSV setup



    Hi Guys,

    I was looking at a McQuay air cooled screw chiller today and was wondering if any of you can elaborate on the pump down setup.

    Rather than the usual llsv, it has a solenoid in the suction line. This solenoid takes liquid from the main liquid line before the tev, it goes through the solenoid once energized and goes to what would be the external eq connection on the tev.

    I'm assuming that the liquid acts against the bellows in the tev and forces it to open?
    When the valve is de-energised it seems to allow the tev to close and thus the system pumps down. However, this solenoid is connected into the suction line. Does the suction pressure act in accordance with this valve to also control the ext eq function of the tev?

    I can't really figure out this strange set up.

    Can anyone elaborate please?



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: McQuay strange pumpdown / LLSV setup

    It sounds like a pilot operated valve.Have a look through this thread from a while back it's all covered
    http://www.refrigeration-engineer.com/forums/showthread.php?31838-Why-the-solinoid-valve&highlight=pilot+operated

    C
    heers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: McQuay strange pumpdown / LLSV setup

    ive looked at a manual and it shows hot gas bypass setup-whats the model number-ive got a few manuals

    Hot Gas Bypass (Optional)
    This option allows the system to operate at
    lower loads without excessive on/off
    compressor cycling. The hot gas bypass option
    is required to be on both refrigerant circuits
    because of the lead / lag feature of the
    controller.
    This option allows passage of discharge gas
    into the evaporator inlet (between the TX valve
    and the evaporator) which generates a false
    load to supplement the actual chilled water or
    air handler load.
    Note:
    The hot gas bypass valve will not
    generate a 100% false load.
    The pressure regulating valve is a Sporlan
    HGBE-8 and factory set to begin opening at
    102 psig with R-410a and can be changed by
    changing the pressure setting. The adjustment
    range is 75 to 150 psig. To raise the pressure
    setting, remove the cap on the bulb and turn the
    adjustment screw clockwise. To lower the
    setting, turn the screw counterclockwise. Do
    not force the adjustment beyond the range it is
    designed for, as this will damage the
    adjustment assembly. The regulating valve
    opening point can be determined by slowly
    reducing the system load while observing the
    suction pressure. When the bypass valve starts
    to open, the refrigerant line on the evaporator
    side of the valve will begin to feel warm to the
    touch.
    The bypass valve includes a solenoid valve that
    is controlled by the MicroTech II controller. It
    is active when the first stage of cooling on a
    circuit is active

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: McQuay strange pumpdown / LLSV setup

    Which model is it?

    Can't see that pipe make-up in their manuals but maybe looking at the wrong ones.

    http://www.mcquay.com/McQuay/home/homepage
    "Literature Search"

    [edit]Go and feed the cat and get beaten to the reply.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2009
    Location
    Sydney
    Age
    38
    Posts
    69
    Rep Power
    15

    Re: McQuay strange pumpdown / LLSV setup

    i have the same system at a site i frequent, the solenoid when energized will feed suction pressure to the external equalizer line on the txv, and when it wants to pump down it de-energizes and instead sends high-side pressure up the external equalizer line, hence forces the txv to shut and pump down.


    edit: just re-read my post and noticed it doesnt explain what i mean so well, so here goes

    we know that a txv has 3 forces in it, 1 opening force and 2 closing forces. the pressure from the bulb, (suction line temperature) is the opening force (as suction line temperature rises it opens the valve to let more refrigerant through). The 2 closing forces are from the superheat spring and the suction pressure from the external equalizer line. With that being said, if u put a higher pressure (from the high side/liquid line) onto the external equalizer line it will force the valve to close, and hence pump the system down.


    the solenoid your talking about (if its what im thinking) is a 3way valve, one line from the suction, one line from the liquid line before the txv and one line going to the external equalizer port on the txv. in normal operation, the valve is energized and is allowing suction pressure up the external equalizer line and operating normally. When the system wants to cycle off/pump down, the valve de-energizes and instead of allowing suction pressure up the equalizer line it instead puts high side/liquid line pressure up it instead, then with the higher pressure on the txv it forces the valve to shut, and the system pumps down. Then once the valve energizes again, it returns the suction pressure back onto the equalizer line, this pressure is alot lower than the bulb pressure due to it having pumped down, the txv opens and lets refrigerant through, and everything starts up again.
    Last edited by Mick13; 22-11-2011 at 07:17 AM.

  6. #6
    Join Date
    Feb 2006
    Location
    Hampshire
    Posts
    61
    Rep Power
    19

    Re: McQuay strange pumpdown / LLSV setup

    Thanks Mick and others.
    Apologies for my late reply.
    I was being a thikko and sussed it out a couple of hours after my post...