    1970's OIL FILLED MAIN SERVICE BRAKER



    I have a main service breaker ( oil filled ) manufactured by Federal Pacific for our High Voltage switch gear 12 kv. There is no oil level or atleast we can't see any oil in any of the 3 sight glasses. I'm not familiar with these old breakers all I know is no oil level on or in anything is not good! Does anyone have any info or suggestions on this matter. I don't think the oil level should really fluctuate at all in these types of service breakers and I don't want this to be left alone very long. I don't have a model number that I can share with you which is what everyone is looking for.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: 1970's OIL FILLED MAIN SERVICE BRAKER

    Its about 30 years old and you want to fix it????/
    Why not replace it with a more modern and safe switch?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 1970's OIL FILLED MAIN SERVICE BRAKER

    Here's some history of those breakers, it seems that they are 'old hat' now-a-days and oil maintenance is critical.

    http://library.abb.com/global/scot/s...0_ENG72dpi.pdf
    Last edited by Brian_UK; 22-11-2011 at 10:48 PM. Reason: Forgot the link
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: 1970's OIL FILLED MAIN SERVICE BRAKER

    as chemi-cool said can't you just replace it
    i myself have never seen one but with it being a breaker i would presume it would be straight forward to replace for a modern switch.
    if this system has this sort of breaker how old is the rest of the electrical circuit has any of the remaining circuit been replaced for more modern switch gear.
    your only as good as your last job

  5. #5
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: 1970's OIL FILLED MAIN SERVICE BRAKER

    Is it possible that these breakers could contain toxic PCBs?

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: 1970's OIL FILLED MAIN SERVICE BRAKER

    the oil acts as an arc arrester, no oil, do not open switch, you could be splattered everywhere. If high voltage get local power supplier to service/preferably replace it.

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: 1970's OIL FILLED MAIN SERVICE BRAKER

    Hi
    as said preveiously do not operate this breaker with out oil.
    i would change this breaker as soon as possible,
    getting oil for this bugger is a pain in the a.......
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: 1970's OIL FILLED MAIN SERVICE BRAKER

    12000 volt switches can only be operated by certified technicians, do not touch it.

  9. #9
    Join Date
    Dec 2010
    Location
    ZA
    Posts
    154
    Rep Power
    16

    Re: 1970's OIL FILLED MAIN SERVICE BRAKER

    The oil is a specialist transformer/switchgear oil, basically a very pure mineral oil with absolutely no additives, and a very low water content. You need a high voltage certified electrician to service it, and at present you will need at least a full flash suit to even operate it. Best is to call the right people to safely service it, as they need to isolate it, switch it off and find the leak that caused it to lose oil in the first place. As a unit dating from the 1970's it could even be a SF6 filled unit, and if the gas has leaked out it it will explode on switching.