condensation water come out from air duct
hello everybody..
need help to trouble shoot the water drop in the ballroom from the air duct
any solution???
thanks.
-
21-11-2011, 09:25 AM #2
Re: condensation water come out from air duct
Hello, a few questions. Are you in a humid environment? Is the system refrigerated? Are you filters dirty..
-
21-11-2011, 10:32 AM #3
Re: condensation water come out from air duct
agreed with cooltech - more information needed.
is it a newly installed system? or have u had it for a while with no issues? (meaning has it been through a summer yet).
if its newly installed, does it have a p-trap?
is the airflow restricted in some way over the indoor coil? does the condensate drain have sufficient fall and is the drain clear?
and.... are u sure its an aircon related problem? iv been called to way too many a/c water leaks that seem to only happen when it rains....
-
21-11-2011, 07:50 PM #4
Re: condensation water come out from air duct
A well insulated duct will not drip! is it insulated on the inside? If not, you're having a big problem.
-
25-11-2011, 04:50 AM #5
Re: condensation water come out from air duct
Thanks for reply bro..
- The system is build around 4 year already, its start after 1 and half year until now and the problem getting bad for this year.
- Ya, malaysia is a humid country, the filter and the air-flow is ok, (even i try to remove the filter for a day but still the same)
- it is possible the system running too cool? i put the setting on return air temp 14 deg C.
-
25-11-2011, 06:54 AM #6
Re: condensation water come out from air duct
what side is the drain on supply or return and does it have a pump? you might need to drop the drain tray out and give the whole system a overhaul
-
25-11-2011, 09:24 AM #7
Re: condensation water come out from air duct
Return air temp 14 deg c. sounds like a coo lroom not a ballroom!! turn that return air set point up to 21 and see how she goes.
-
28-11-2011, 04:50 PM #8
Re: condensation water come out from air duct
That is no drain for supply and return air duct,
Ya, some times people will complain that is too cool...
I reset the return air set point to 19deg C and its work, i think i should increase to 21 like cool_tech say and see first.
thanks for helping ..