    Frequent defrost Daikin FTXL35



    Anyone know the precise condition for defrost in the Daikin FTXL35 heatpump?
    They seem to run defrost every 30 min without any reason, even no ice and low load.



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Frequent defrost Daikin FTXL35

    Conditions for Starting Defrost
    The starting conditions must be made with the outdoor air temperature and heat exchangertemperature. Under the conditions that the system is in heating operation, 6 minutes after thecompressor is started and more than 44 minutes of accumulated time pass since the start of theoperation or ending the defrosting.
    Conditions for Canceling Defrost
    The judgment must be made with heat exchanger temperature. 4c-12c

  3. #3
    Join Date
    Dec 2011
    Location
    Norway
    Posts
    2
    Rep Power
    0

    Re: Frequent defrost Daikin FTXL35

    I've found this information earlier. It would be of great help to know for what outdoor temp and for what exchanger temp the condition is set.