    r408 a



    hi
    can anyone tell me were i can get superheat and subcooling charts for the above gas and what the ideal temps are in a freezer room .



  2. #2
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: r408 a

    coolpack but a freezer that works with this gas, it is time to change with the new gas

  3. #3
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: r408 a

    R408 is no longer in use
    there are threads on this site with people using R408 and R22 why are people using these gases they should be retrofitting these systems.
    if you have broken into this system it will require retrofitting.
    your only as good as your last job

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: r408 a

    Quote Originally Posted by cold.man View Post
    R408 is no longer in use
    there are threads on this site with people using R408 and R22 why are people using these gases they should be retrofitting these systems.
    if you have broken into this system it will require retrofitting.
    Maybe not in South Africa..??


    ++

    PT Chart ...

    http://www.refrigerants.com/pics/ptchart.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Nov 2011
    Location
    south africa
    Age
    56
    Posts
    4
    Rep Power
    0

    Re: r408 a

    HI in sa we still use r22 in most of our commercial applications as well as 406 and 408,what i was asking is if my room is at minus 20 degrees c my vapour pressure at the compressor should be around 26 psi what then should the temp be on the suction line at the compressor and at the exit of the evaporator .what should they be?? for the superheat to be ideal

  6. #6
    Join Date
    Jul 2011
    Location
    United States of America
    Age
    59
    Posts
    86
    Rep Power
    13

    Re: r408 a

    Suction line temp at compressor is not where you measure superheat. You should measure at the evaporator outlet. This is probably a low temp system, so 6 to 8 degree superheat when the box is at temp. Suction line temp at compressor can vary depending on heat picked up travelling to compressor. Usually 40 degrees Fahrenheit or lower is ideal for compressor cooling.

  7. #7
    Join Date
    Nov 2011
    Location
    south africa
    Age
    56
    Posts
    4
    Rep Power
    0

    Re: r408 a

    thanks texas
    is there a chart that tells you the superheat should be 6 to 8 how do you determain what the correct superheat should be ,im not asking how to measure it but what the correct temps should be for different gasses and systems

  8. #8
    Join Date
    Jul 2011
    Location
    United States of America
    Age
    59
    Posts
    86
    Rep Power
    13

    Re: r408 a

    Check this out from Sporlan---- http://sporlanonline.com/10-9_32011.pdf

    Sporlan is the number one manufacturer of refrigeration valves and products.

    http://sporlanonline.com/tevs.shtml

    Hope it helps...

    James

  9. #9
    Join Date
    Nov 2011
    Location
    south africa
    Age
    56
    Posts
    4
    Rep Power
    0

    Re: r408 a

    thanks will do

    cliff
    coldfact

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •