Results 1 to 7 of 7
Thread: Daikin H4 Fault code
-
19-11-2011, 04:02 PM #1
Daikin H4 Fault code
Hey all. I'm due at a job in the morning with a Daikin showing a H4. Thanks to this site I found out that it's the Outdoor LP Switch.
Am I ok to loop it out to test to see if the switch itself is faulty?
Thanks
-
19-11-2011, 04:31 PM #2
Re: Daikin H4 Fault code
Welcome Eire1.
Provided you put your gauges on to confirm you do not have a lp situation.
Logic would say a quick run would not harm.
Grizzly.Last edited by Grizzly; 19-11-2011 at 04:33 PM.
-
19-11-2011, 05:28 PM #3
Re: Daikin H4 Fault code
Yeah, I'll see what kind of pressure I'm getting. It has to be the gas or switch itself really.
Thanks Grizzly
-
19-11-2011, 06:51 PM #4
Re: Daikin H4 Fault code
Could be the PCB thats faulty i've had that before
-
19-11-2011, 08:02 PM #5
Re: Daikin H4 Fault code
I hope it's not the PCB. Sure I'll find out in the morning.
-
19-11-2011, 10:11 PM #6
Re: Daikin H4 Fault code
h4 -lp fault-ive had transducers fail,also ive got 1 with a lev not opening-not checked it properly yet
-
20-11-2011, 11:52 AM #7
Re: Daikin H4 Fault code
No gas in the system at all. Hope this leak isn't too hard to find.