    Oil separator
    How and when the compressor sucks the oil back from oil separator ?
    Moises
    Jul 2009
    Illinois
    187
    15
    Re: Oil separator
    There is a float inside the seperator, it opens when enough oil is available to return to compressor.
    Dec 2008
    Brazil
    106
    Re: Oil separator
    Thanks Emmett
    So you mean the compressor is always make sucction action and the separator's float releases the oil ?
    Is the separator return line linked to the same chamber of compressor sucction line ?
    Moises
    Somerset
    69
    4,697
    Re: Oil separator
    Acrisoft.
    I am confused because the oil separator is normally on the discharge side of the system.
    And therefore the oil is being pushed to-wards the compressor via the oil return line under discharge gas pressure.
    Yes you can get some oil return via the suction which is carried over provided the refrigerant gas swept volume is sufficient.
    But the amount is minimized due to the oil recovery via the oil separator on the discharge side of the system.
    Just what size of system are you referring to?
    Are you looking at a slop pot? Which is something entirely different.
    11,025
    Re: Oil separator
    There is some useful information on the Sporlan Literature website which might be worth reading through, maybe it will answer some of your questions.
    http://www.sporlanonline.com/oilcontrol.shtml
    Feb 2009
    telford
    2,092
    33
    Re: Oil separator
    a "slop pot" love them descriptions
    Somerset
    69
    4,697
    Re: Oil separator
    Quote Originally Posted by cadwaladr View Post
    Surely a Shropshire lad such as yourself would know that one?
    No point in going round the Wrekin!
    Sep 2009
    Iran
    66
    672
    1
    Re: Oil separator
    in inside of some oil separator is float vales , so when oil reach to that level it open and let oil goes back to crankcase of compressor ,
    also in some of oil separator if we do not have that system we use this system we have solenoid valve with orifice on it ( solenoid valve energized when compressor running) in the returning oil pipe from oil separator to compressor.
    Jul 2010
    manchester
    212
    15
    Re: Oil separator
    discharge from comp through the oil sep, the sep picks up oil from the discharge from comp
    depending on the oil set up, dont confuse the oil sep for the oil rez.
    you can also have a suction accumalator ie slop pot.
    you can have a set up where you have an oil sep and oil will be fed from the bottom of sep to comps this is usally on smaller set ups. on larger from sep to oil rez.
    or you could have suction accumalator ie slop pot and fed from the bottom of the slop pot to comps.
    these little holes in the bottom of the slop pot or oil sep can be prone to blocking.