    good night

    I had a problem with a quantum panel lx unexpectedly shuts down and the compressor will restart again put into operation panel and the compressor, and to replace the flash card and the problem persists.

    I will appreciate any help possible!

    thanks



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: panel quantum lx

    check your pressures (low- hi & oil). when it is running and goes to off,

  3. #3
    Join Date
    Nov 2011
    Location
    USA
    Age
    69
    Posts
    3
    Rep Power
    0

    Re: panel quantum lx

    I also have a LX that will unexplained will re-boot! Now I was the YPS start-up guy for my area for afew years, and the factory engineers didnt give me a answer that cured the problem! While this particular machine was in waranty I change wire harness, power supply, grounding confired, and finally the mother board. After it had went out of warranty problem started again, mother board changed again! Does your machine have communications set up to plant DDC? When mother board is changed problem goes away for a while but comes back. I have several LXs we take care of now and have seen this only on three of them. email me at byoung725@netzero.net as I am interested if you have some other symtoms.