    Qualitaire Heat Pump



    Hello,

    Hope someone can help.

    This is a wiring diagram from a split system heat pump Qualitaire. The unit Model No etc has worn so unfortunately I am unable to provide this information.

    At present the unit is wired to cool only (connection C). The customer now wants to have it for heating also.

    The unit is connected to an Eberle controller, which has the facility to provide 240volts to the reversing valve (connection RV). Do i need to provide a permanent 240 volt to the connection H for the defrost activation.

    Please see picture. Thanks in advanceQualitaire Wiring Diagram.jpg



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Qualitaire Heat Pump

    Sorry, where is connection 'H'?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Qualitaire Heat Pump

    found this on eaton williams website
    ICU CONDENSING UNIT INSTALLATION MANUAL
    September2003:E\Manuals\Others\Qualitair\ICC\0412118 8
    6. POWER & CONTROL CONNECTIONS
    ICU SINGLE PHASE COOLING ONLY
    ICU Terminal Customer Connections
    PE Customer Earth Connection
    E
    N Customer Neutral Connection
    L Customer Live Connection
    C Cooling Signal (From Indoor Unit)
    S Motor speed control sensor
    ICU SINGLE PHASE HEAT PUMP
    ICU Terminal Customer Connections
    PE Customer Earth Connection
    E
    N Customer Neutral Connection
    L Customer Live Connection
    C Cooling Signal (From Indoor Unit)
    S Motor speed control sensor
    RV Heating signal (from Indoor unit)
    H Heating Signal (From Indoor Unit) – defrost heating.

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Qualitaire Heat Pump

    Could it be that the terminal thought to be 'R' is actually 'H'.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  5. #5
    Join Date
    Jul 2006
    Location
    essex
    Posts
    31
    Rep Power
    0

    Re: Qualitaire Heat Pump

    Sorry guys, the terminal marked as R should be H. That's what you get for posting at 23:37.Sorry.