    Part Winding issue



    I currently have a CSH6563-40 bitzer Screw compressor that uses the part windings configuration to start up not sure as to why the start contactor /overload has failed. If the compressor is rated at 65 full rated amps what amp rating should the first contactor & overload be rated at? What amp rating should the second contactor and overload be rated at the timer is set 0.2 sec to interlock the run contactor ?

    The current overloads are Schneider LRD33 and Contactors are LCI50D have the correct switching gear been selected ?



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Part Winding issue

    Hi
    are you sure its a part winding start, and not a two contactor wye delta starter?
    if it is indeed part winding what is the ratio?60-40 50-50??
    this will determin the setting?
    what kind of unit is this comp in?
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Part Winding issue

    Hi if the winding is p/wind then its 50% /50% so both contactors and overloads should be the same

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Part Winding issue

    Hi Siphon.
    Goshen and Ghaz are spot on.
    You first need to determine the start wind ratio.
    As you state the contactors are the same size, I think it's safe to assume that you have a 50% 50%
    Winding ratio.
    With Bitzer for 50/50 your contactor needs to be rated at 60% Max Running Amps.
    Whereas if it were a 60/40 part wind then the sizing is 70% and 50% max running amps.

    I hope this further helps?
    Grizzly

  5. #5
    Join Date
    Aug 2009
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: Part Winding issue

    Quote Originally Posted by goshen View Post
    Hi
    are you sure its a part winding start, and not a two contactor wye delta starter?
    if it is indeed part winding what is the ratio?60-40 50-50??
    this will determin the setting?
    what kind of unit is this comp in?
    good luck
    I am a little confused in the 2 different configurations what is the difference in the two?

    1. Part-windings
    2. Start windings well was well explanined in my previous post http://www.refrigeration-engineer.co...th-multi-speed

  6. #6
    Join Date
    Apr 2010
    Location
    australia
    Age
    45
    Posts
    78
    Rep Power
    15

    Re: Part Winding issue

    i may be wrong but there should only 1 overload i think. the part winding contators pull in very quick .5> 1sec the current will be high but only for a sec. check the wiring diagram for a bizter

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Part Winding issue

    Attachment 8269

    Ok.
    The bible according to Bitzer.
    Or at least what I have found so far.
    It may help?

    Also follow this link and then select your relevant screw comp.
    Then you can download the necessary manual, which will have definitions of the standard part wind setup.
    http://www.bitzer.de/eng/products/docu/doc_det/12

    Grizzly
    Last edited by Grizzly; 04-11-2011 at 10:07 PM.

  8. #8
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Part Winding issue

    Hi grizzly
    nice posting !!!
    best regards
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  9. #9
    Join Date
    Aug 2009
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: Part Winding issue

    Well illustrated and spot on info, just what i needed to make the troubleshooting easier

  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Part Winding issue

    Each part winding to have a separate overload relay .
    Olr to be set practically on the current drawn .
    Contactor rating to be 70% of max current ....... For each of the part winding

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Part Winding issue

    Quote Originally Posted by D.D.KORANNE View Post
    Each part winding to have a separate overload relay .
    Olr to be set practically on the current drawn .
    Contactor rating to be 70% of max current ....... For each of the part winding
    DD have you bothered to read any of the other posts?

    Grizzly

  12. #12
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Part Winding issue

    We usually do the interlocking of part winding .... That is if first winding fails during operation of compressor the second winding is disconnected via control circuit to avoid the compressor to operateon only one 50 pc winding . This will shut down the comp

  13. #13
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Part Winding issue

    Hi ive never seen interlocking on p/wind because if one half goes the motor is no good and needs to be replaced any way, were as star delta are has a lock between star and delta contactor so the contactors don,t come in same time and blow

  14. #14
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Part Winding issue

    Quote Originally Posted by GHAZ View Post
    Hi ive never seen interlocking on p/wind because if one half goes the motor is no good and needs to be replaced any way, were as star delta are has a lock between star and delta contactor so the contactors don,t come in same time and blow
    Hi
    you may not of noticed a mechanical interlock ,but many old machines have a timer that prevents compressor from working if the two contactors of part winding dont engage ,the newer units have a digital input telling the controller if one stage didnt engage!
    i personally try to convert all these part windings and star delta to a one stage start using a soft starter
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!