    Daikin Q VRV replacement unit



    Hi chaps

    Anyone got any experience of these bad boys both from installing and operational after care?
    http://www.daikin.co.uk/r22-refrigerant/default.jsp

    TIA :-)

    Richard
    Last edited by r.bartlett; 17-11-2011 at 11:45 AM.



  2. #2
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Daikin Q VRV replacement unit

    Quote Originally Posted by r.bartlett View Post
    Hi chaps

    Anyone got any experience of these bad boys both from installing and operational after care?
    http://www.daikin.co.uk/r22-refrigerant/default.jsp

    TIA :-)

    Richard

    The best option for replacing old Daikin R22 VRV systems.

    Heat Pump - Options

    1. Change outdoor only and keep indoor units if no older than K-series. (check with DUK first).
    2. Change outdoor and indoor units.

    Heat Recovery - Options

    1. Change outdoor, BS units and keep indoor units, again, same as above applies.
    2. Change outdoor, BS units and indoor units.

    Refnets

    1. Check existing refnets are installed correctly before replacing any of the old system with new.
    2. Check that the distance between the first refnet and the furthest fan coil isn't above 40 metres (measuring the route of the pipe work).

    BS boxes

    1. Brazed connections.
    2. 5 expansion valves these assist with maintaining system duty while in change-over operation.
    3. Check and double check the installation of each, LP(suction), HP/LP(discharge or suction) & liquid pipe connection (if you hear the sound of a vuvuzela in heating operation you'll know you've crossed the pipes)!

    Outdoor unit(s)

    1. Check and double check the installation of each, LP(suction), HP/LP(discharge or suction) & liquid pipe connection
    2. Each module requires it's own independant circuit breaker if installaing a twin, triple or quad outdoor system.
    3. If installing a multi module, read the refnet installation guide!
    4. It has H/P switch of 33 bar. Pressure test around this range.

    Test run

    1. Test run will carry out piping/wiring check, contamination operation and system auto charge so read and understand the manual before any test run is carried out.
    2. Once the test run is complete you set a dip switch to isolate the contamination filter from system.
    Last edited by AbsoluteWDJ; 17-11-2011 at 09:23 PM. Reason: grammer

  3. #3
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin Q VRV replacement unit

    big thanks.
    have you seen one running?

  4. #4
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Daikin Q VRV replacement unit

    Quote Originally Posted by r.bartlett View Post
    big thanks.
    have you seen one running?

    I've seen a few in operation. They are pretty much the same as a VRV III with regard operation. If you are looking to replace an existing R22 VRV then this option would reduce in installation cost and time.