    Exclamation Fujitsu forced cooling help?



    Hi Guys,

    Dont usually do too much with fujitsu kit so was just wondering if anyone can help. Iv got a customer who has the follwing condenser model no's
    AOYR24LCC
    AOYS12LDC
    AOYR18LCC

    The customer wants to have the systems as cooling only as the office staff are running them in heating mode aswel as having the radiators on.

    Is this possible on these model no's? Dip switch on the condenser?

    Any help would be great.

    Thanks in advance.



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Fujitsu forced cooling help?

    Might be simpler to disconnect the 4 way solenoid coil? i think it energises to heat, although with rads why are they running the heat pumps? Not enough heat output, might be cheaper to run the heat pumps?

    al
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Dec 2008
    Location
    England
    Age
    36
    Posts
    20
    Rep Power
    0

    Re: Fujitsu forced cooling help?

    Apparently the girls are moaning so they turn the heating on and the heat pumps so its like a furnace in there and the boss is getting the hump! Would disconnecting that not cause the system to fault?

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Fujitsu forced cooling help?

    If they put it to heating it will fault due to no heat, actually it's a ****e way to do it, no point in wasting energy cooling them. Have you checked fgeurofred for literature?

    al
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Fujitsu forced cooling help?

    whooaaah there, simply fit a tamperproof stat to disable power to the indoor at say 22deg, so the system will provide heat but not excessivly, mauling with the 4 way valve will mean in heating mode, the system will cool and cause freeze up of the indoor coil as the indoor will be in low fan mode waiting for a coil temp of 33deg,system tthen provides some cooling but then will run continuously as the setpoint of say 23 isnt going to be reached!!

  6. #6
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Fujitsu forced cooling help?

    bang on install, that's exactly what i was suggesting) good idea man, pity me rep points are all dried up!

    al
    Mostly found in the southern part of this green and pleasant land.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fujitsu forced cooling help?

    Can't see anything useful in the manuals for that problem.

    Why not just remove all of the remote controllers during the winter peiod?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Fujitsu forced cooling help?

    brian- have u tried taking a remote control off a woman-let alone a tribe of women- an as for a controller that operates heat-not even steve irwin would have a go at that!
    Quote Originally Posted by Brian_UK View Post
    Can't see anything useful in the manuals for that problem.

    Why not just remove all of the remote controllers during the winter peiod?