    carrier xarios y micro voltage



    are these micro,s voltage sesitive a supplier has sent me a new one when i asked for a 24 volt one his answer was they are all the same voltage? want to check before I fry it!!



  2. #2
    Join Date
    Aug 2013
    Location
    uk
    Posts
    17
    Rep Power
    0

    Re: carrier xarios y micro voltage

    Micro works with 12 or 24 volts.
    You just have to set the configs on the display to correct voltage...

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: carrier xarios y micro voltage

    ok many thanks

  4. #4
    Join Date
    Dec 2004
    Location
    U.K
    Age
    55
    Posts
    518
    Rep Power
    21

    Re: carrier xarios y micro voltage

    Quote Originally Posted by UKengineer View Post
    Micro works with 12 or 24 volts.
    You just have to set the configs on the display to correct voltage...
    what he says, just press the hidden button on the cab control and set to 24V.

    No problems, but drop me a note next time you need one as have loads of good used.

  5. #5
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: carrier xarios y micro voltage

    shoot just got a new one last week,la de dah!

  6. #6
    Join Date
    Jul 2009
    Location
    uk
    Posts
    5
    Rep Power
    0

    Re: carrier xarios y micro voltage

    hi i have a problem on xarios 500. i got dead display, when i swap the dead one with on the other working unit it works there. any help/ wiring diagram.
    cheers

  7. #7
    Join Date
    Sep 2006
    Location
    england
    Posts
    285
    Rep Power
    18

    Re: carrier xarios y micro voltage

    depending on age inside micro is a 1amp fuse it looks like a little capacitor pull out check with meter on newer models there are 2 fuses

  8. #8
    Join Date
    May 2011
    Location
    Romania
    Age
    40
    Posts
    84
    Rep Power
    13

    Re: carrier xarios y micro voltage

    Also check cable and +12v on pin 4 from ignition