    Capillary Connectors
    Hi All,
    Any one having problems with capillary connectors used on pressure controls?
    I have 6-7 high & low pressure controls in 1 system.
    All are not behaving as per the system pressure.
    These are flexible connectors with 1/4" OD.
    Any views!!!
    Somerset
    64
    4,582
    Re: Capillary Connectors
    Air in the system by any chance?
    Jun 2009
    Lusk , Dublin
    1,120
    Valve depressors where they should be ???
    Stu
    Tool's ? check ! Condom's ? check !
    Oct 2003
    56
    5,519
    28
    What's your problem exactly with those? Are they leaking, breaking, ...
    Reaction to slow? Oil in it.
    Apr 2006
    Canada
    48
    152
    13
    Problem is that controls are not working as per system pressure!!
    We used 1/2" flexible hoses, where inside dia is approx 2 mm.
    Wondering, if we should use 1/4" copper tubing!
    Somerset
    64
    4,582
    If the bore is 2mm then you may well be getting poor reactive times / pressures.
    With the gas flow being dampened.
    As you suggest yourself.
    Try one line with copper and see if things improve?
    An easy way of proving things.