    Hi All
    Can anyone tell me how Heat Rejection Factors are obtained for 100% suction-cooled hermetically sealed compressor? Some manufacturers do not provide such data in their catalogue anymore.
    Freddy
    Mar 2005
    58
    110
    Re: Heat Rejection Factor
    This depends on the construction of the compressor and on the application. A good estimation will be about 5% of the absorbed power.
    Feb 2001
    Tampa Florida
    1,076
    My recollection is that it is about 3% less than absorbed power (compressor wattage). This is the assumed reduction through the compressor body and discharge piping to the ambient. A safe number, methinks.
    Feb 2001
    Tampa Florida
    1,076
    I suppose I didn't answer the original question all that well. If you look at the compressor wattage versus capacity you have a ratio which changes significantly between the major suction pressures represented by Low Temperature, Medium Temperature, and High Temperature applications. The heat rejection factor is a way of representing that ratio that you can apply to the capacity of the compressor. It's really just an approximation of the input/output ratio.
    The wattage input represents all the heat that you must reject with suction cooled semi-hermetic compressors. My ealier (3%) comment referred to fudging this number down for heat loss before the condenser.
    Feb 2005
    Malaysia
    7
    Thank you for the valuable information.
    By the way, Dan. Is there an industry standard to classify the different ranges of evaporating temperature?
    I am refering to Low Temp, Medium Temp, and High Temp. It seems that different compressor manufacturer uses a slightly different ranges of temperature in their catalogue.
    Freddy
    Feb 2001
    Tampa Florida
    1,076
    Regarding the difference between the operating temperature range classifications, it is rather arbitrary, since many semi-hermetic compressors can operate across rather broad temperature ranges. For convenience, I think of the ranges as such:
    • Ultra low temperature below -40 deg F
    • Low temperature -40 to -10 deg F
    • Medium temperature - 5 to 25 deg F
    • High temperature/air conditioning 30 and above
    I am not aware of an industry standard, nor do I see the need for one.
    Jun 2005
    California
    394
    Freddy, This may be of some help for you
    http://66.28.63.222/documents/Conden...550rpm_630.pdf
    Feb 2005
    Malaysia
    7
    Thanks Pal
    Nice piece of information.
    Freddy
    jaimebuiles2's Avatar
    jaimebuiles2 Guest
    It depends from the evaporator and condensing temperature. You can find tables like that for open compressors, but it's for hermetic compressors. I hope it can help you.
    SUCTION COOLED HERMETIC COMPRESSORS
    EVAPORATOR TEMP (F)
    CONDENSING TEMPERATURE (F)
    90
    100
    110
    120
    130
    140
    -40
    -30
    -20
    -10
    1.66
    1.57
    1.49
    1.42
    1.73
    1.62
    1.53
    1.46
    1.80
    1.68
    1.58
    1.50
    2.00
    1.80
    1.65
    1.57
    1.64
    5
    10
    1.36
    1.53
    1.31
    1.40
    1.37
    1.34
    1.44
    1.41
    1.38
    1.50
    1.46
    1.43
    1.56
    1.52
    1.49
    1.62
    1.59
    1.55
    1.28
    1.26
    1.24
    1.32
    1.29
    1.27
    1.35
    1.33
    1.31
    1.40
    1.37
    1.35
    1.46
    1.43
    1.40
    1.52
    1.49
    1.45
    30
    40
    1.22
    1.18
    1.14
    1.25
    1.21
    1.47
    1.28
    1.24
    1.20
    1.32
    1.27
    1.23
    1.37
    1.31
    1.26
    1.42
    1.35
    1.29
    *Outside of normal limits for single stage compressor application.
    jaimebuiles2 Guest
    Nov 2005
    New Zealand
    550
    Quote Originally Posted by jaimebuiles2 View Post
    Geez man this post is over 5 years old
    May 2006
    India
    399
    I usually take it as heat equivalent ( in kw ) of evaporator capacity + motor kw as the heat rejection capacity of condenser . Besides, i keep the allowance for max sst expected after fresh start up .
  1. Suction gas <-> liquid line heat exchange and performance gains
    Last Post: 18-05-2010, 01:52 PM
  2. frostles heat pump
    Last Post: 31-03-2008, 07:53 AM
  3. heat pump capacity adjust
    Last Post: 14-02-2006, 07:32 AM
  4. Dx coil design
    By abbasi in forum Technical Discussions
    Last Post: 16-12-2004, 12:41 AM
  5. R134a <-> liquid heat exchanger design
    Last Post: 10-05-2002, 08:36 AM