    Heat Rejection Factor



    Hi All

    Can anyone tell me how Heat Rejection Factors are obtained for 100% suction-cooled hermetically sealed compressor? Some manufacturers do not provide such data in their catalogue anymore.

    Cheers
    Freddy



  2. #2
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Heat Rejection Factor

    Hi,
    This depends on the construction of the compressor and on the application. A good estimation will be about 5% of the absorbed power.

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Heat Rejection Factor

    My recollection is that it is about 3% less than absorbed power (compressor wattage). This is the assumed reduction through the compressor body and discharge piping to the ambient. A safe number, methinks.

  4. #4
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Heat Rejection Factor

    I suppose I didn't answer the original question all that well. If you look at the compressor wattage versus capacity you have a ratio which changes significantly between the major suction pressures represented by Low Temperature, Medium Temperature, and High Temperature applications. The heat rejection factor is a way of representing that ratio that you can apply to the capacity of the compressor. It's really just an approximation of the input/output ratio.

    The wattage input represents all the heat that you must reject with suction cooled semi-hermetic compressors. My ealier (3%) comment referred to fudging this number down for heat loss before the condenser.

  5. #5
    Join Date
    Feb 2005
    Location
    Malaysia
    Posts
    7
    Rep Power
    0

    Re: Heat Rejection Factor

    Thank you for the valuable information.

    By the way, Dan. Is there an industry standard to classify the different ranges of evaporating temperature?
    I am refering to Low Temp, Medium Temp, and High Temp. It seems that different compressor manufacturer uses a slightly different ranges of temperature in their catalogue.

    Cheers
    Freddy

  6. #6
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Heat Rejection Factor

    Regarding the difference between the operating temperature range classifications, it is rather arbitrary, since many semi-hermetic compressors can operate across rather broad temperature ranges. For convenience, I think of the ranges as such:

    • Ultra low temperature below -40 deg F
    • Low temperature -40 to -10 deg F
    • Medium temperature - 5 to 25 deg F
    • High temperature/air conditioning 30 and above


    I am not aware of an industry standard, nor do I see the need for one.

  7. #7
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Heat Rejection Factor

    Freddy, This may be of some help for you
    http://66.28.63.222/documents/Conden...550rpm_630.pdf

  8. #8
    Join Date
    Feb 2005
    Location
    Malaysia
    Posts
    7
    Rep Power
    0

    Re: Heat Rejection Factor

    Thanks Pal

    Nice piece of information.

    Cheers
    Freddy

  9. #9
    jaimebuiles2's Avatar
    jaimebuiles2 Guest

    Heat Rejection Factor

    It depends from the evaporator and condensing temperature. You can find tables like that for open compressors, but it's for hermetic compressors. I hope it can help you.

    SUCTION COOLED HERMETIC COMPRESSORS
    EVAPORATOR TEMP (F)
    CONDENSING TEMPERATURE (F)
    90
    100
    110
    120
    130
    140
    -40
    -30
    -20
    -10
    1.66
    1.57
    1.49
    1.42
    1.73
    1.62
    1.53
    1.46
    1.80
    1.68
    1.58
    1.50
    2.00
    1.80
    1.65
    1.57
    *
    *
    *
    1.64
    *
    *
    *
    *
    0
    5
    10
    1.36
    1.53
    1.31
    1.40
    1.37
    1.34
    1.44
    1.41
    1.38
    1.50
    1.46
    1.43
    1.56
    1.52
    1.49
    1.62
    1.59
    1.55
    15
    20
    25
    1.28
    1.26
    1.24
    1.32
    1.29
    1.27
    1.35
    1.33
    1.31
    1.40
    1.37
    1.35
    1.46
    1.43
    1.40
    1.52
    1.49
    1.45
    30
    40
    50
    1.22
    1.18
    1.14
    1.25
    1.21
    1.47
    1.28
    1.24
    1.20
    1.32
    1.27
    1.23
    1.37
    1.31
    1.26
    1.42
    1.35
    1.29

    *Outside of normal limits for single stage compressor application.

  10. #10
    jaimebuiles2's Avatar
    jaimebuiles2 Guest

    Re: Heat Rejection Factor

    It depends from the evaporator and condensing temperature. You can find tables like that for open compressors, but it's for hermetic compressors. I hope it can help you.

  11. #11
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Heat Rejection Factor

    Quote Originally Posted by jaimebuiles2 View Post
    It depends from the evaporator and condensing temperature. You can find tables like that for open compressors, but it's for hermetic compressors. I hope it can help you.
    Geez man this post is over 5 years old
    My wife used to say you never listen to a word I say at least I think that what she said

  12. #12
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Heat Rejection Factor

    I usually take it as heat equivalent ( in kw ) of evaporator capacity + motor kw as the heat rejection capacity of condenser . Besides, i keep the allowance for max sst expected after fresh start up .

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. heat pump capacity adjust
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 14-02-2006, 07:32 AM
  4. Dx coil design
    By abbasi in forum Technical Discussions
    Replies: 11
    Last Post: 16-12-2004, 12:41 AM
  5. R134a <-> liquid heat exchanger design
    By DaBit in forum Technical Speculations
    Replies: 19
    Last Post: 10-05-2002, 08:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •