Results 1 to 3 of 3
  1. #1
    Join Date
    Sep 2008
    Location
    new zealand
    Posts
    21
    Rep Power
    0

    Cool required technical support of mitsubishi wall mounted heat pump



    Hi I have a problem of Mitshishi elect. wall mount heat pump problem,
    operation in cool mode is okay, but cannot operate in heat mode, the compressor and outdoor fan were not running,
    indoor model: MSZ-GB50VA-A1
    outdoor model: MUZ-GB50VA-A1
    I have check the fault from remote control with prsee the mode, too cool and set button, but the indoor unit, the light of operation and indicator were both off, so we go to check the outdoor unit, and the red LED 1 is 5 times flash and 2.5 second off, we have checked all the thermistor all are okay, so anyone give advice what is wrong.
    Thanks for your kind attention.
    Regards
    Otto



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: required technical support of mitsubishi wall mounted heat pump

    you have mail

  3. #3
    Join Date
    Sep 2008
    Location
    new zealand
    Posts
    21
    Rep Power
    0

    Re: required technical support of mitsubishi wall mounted heat pump

    Thanks,I have received the manual from BDT new zealand, so I will check the manual first and if I still got the problem, I will ask your professional advice.
    Thanks for your assistance.
    Regards
    Otto

Posting Permissions