Results 1 to 10 of 10
Thread: can any body help with this
11-11-2011, 09:01 PM #1
Supaheat: 26degs,
Evap: -11degs.
Condens: 48degs.
Compressor: 126degs (thats our GT6 sensor when it alarmed).
GT10: 12degs (ground loop in).
GT11: 7.5degs (ground loop out).
Heavy frosting on expansion valve, which would defrost in my hand but after about a minute. Would expect a much quicker response.
No subcooling temps.
the gas is 407c
11-11-2011, 09:04 PM #2
Re: can any body help with this
faulty tev/orifice blocked
12-11-2011, 07:38 AM #3
Hi Thanks install monkey! Can you explain why its the TEV and not an undercharge?
12-11-2011, 09:29 AM #4
heavy frosting on thr tev and ur condenser is 48deg,what are ur running pressures
12-11-2011, 11:28 AM #5
hi hes not sent me running pressures but has adjusted valve and now getting these readings
Supaheat: 15degs.
Evap: -3degs.
Condens: 52degs.
Compressor: 110degs.
No frosting on expansion valve.
what pressures should we be looking at?
the system has been running fine for 12 months prier to this.
12-11-2011, 11:47 AM #6
what should super heat be?
12-11-2011, 12:03 PM #7
Superheat 6...10K
Subcooling 5...8 K
12-11-2011, 10:03 PM #8
have you checked your liquid line sight glass?
how does you liquid line drier feel?
15k still is a wide superheat.
restriction
or short of gasyour only as good as your last job
13-11-2011, 01:57 AM #9
Hi Cold Man thanks
I suggested that it might be short of gas, but he did not check the sight glass yet
Can you explain how u would tell the difference between whether it was the tev or undercharge?
I know that the system has all been sized properly, and has been running fine for nearly a year
The frosting and the high compressor reading made me think its not getting enough gas but I don't know what the different symptoms would be for whether its a tev restriction or undercharge. I don't think the tev was set wrong but I know they can sometimes need adjustment - but would that be after a year?
Dont know if am making sense now as it the middle of the night
13-11-2011, 08:19 PM #10
It's allright thanks - I got it. I was just getting myself confused