Results 1 to 8 of 8
  1. #1
    Join Date
    Nov 2011
    Location
    Norway
    Posts
    1
    Rep Power
    0

    Vacuuming in foggy and cold weather



    Hi all.

    Anyone has experience in vacuuming the cobber tubes in foggy and cold weather, or should one avoid such condition?

    Please share your experience.

    Regards

    M



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Vacuuming in foggy and cold weather

    Sometimes you have no choice.
    But the lower the ambient and the wetter the atmosphere that any install may of been subjected to.
    The lower the vacuum needed to eradicate any moisture.
    Grizzly

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Vacuuming in foggy and cold weather

    Purge the tubing with OFN and then carry out a triple evacuation, breaking the vacuum with OFN at each stage.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Vacuuming in foggy and cold weather

    You can also heat the system with hot water or even with a torch.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Vacuuming in foggy and cold weather

    link the lp switch,compressor overheat stat and run the new system to push the moisture out-speeds up the vaccing process

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Vacuuming in foggy and cold weather

    Quote Originally Posted by install monkey View Post
    link the lp switch,compressor overheat stat and run the new system to push the moisture out-speeds up the vaccing process
    That will require an experienced engineer or the compressor will burnout.

  7. #7
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,120
    Rep Power
    25

    Re: Vacuuming in foggy and cold weather

    You will need a hat,scarf ,warm jacket and a pair of gloves.
    And a torch with a yellow lens.

    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  8. #8
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Vacuuming in foggy and cold weather

    Hello

    You should use a steam chart and read off the depth of vacuum for the ambient temperature at the coldest part of the system. You wont be able to pull a satisfactory vacuum if any pipework is below 0c.

    There's no need to pull such a deep vacuum in hot weather, its a waste oftime.

    Triple vac just speeds the process up, it wont increase the depth of the vacuum.

    Regards
    Last edited by Contactor; 03-01-2012 at 01:03 AM. Reason: .