    Nov 2011
    Norway
    1
    Vacuuming in foggy and cold weather
    Hi all.
    Anyone has experience in vacuuming the cobber tubes in foggy and cold weather, or should one avoid such condition?
    Please share your experience.
    M
    4,697
    Re: Vacuuming in foggy and cold weather
    Sometimes you have no choice.
    But the lower the ambient and the wetter the atmosphere that any install may of been subjected to.
    The lower the vacuum needed to eradicate any moisture.
    Dec 2008
    564
    Purge the tubing with OFN and then carry out a triple evacuation, breaking the vacuum with OFN at each stage.
    Sep 2003
    ISRAEL
    72
    4,248
    You can also heat the system with hot water or even with a torch.
    manchester
    5,639
    link the lp switch,compressor overheat stat and run the new system to push the moisture out-speeds up the vaccing process
    Sep 2003
    ISRAEL
    72
    4,248
    That will require an experienced engineer or the compressor will burnout.
    Jun 2009
    Lusk , Dublin
    1,115
    You will need a hat,scarf ,warm jacket and a pair of gloves.
    And a torch with a yellow lens.
    Stu
    Scotland
    327
    Hello
    You should use a steam chart and read off the depth of vacuum for the ambient temperature at the coldest part of the system. You wont be able to pull a satisfactory vacuum if any pipework is below 0c.
    There's no need to pull such a deep vacuum in hot weather, its a waste oftime.
    Triple vac just speeds the process up, it wont increase the depth of the vacuum.
