    Dec 2008
    Brazil
    106
    Charge R134 without a scale
    I know that a scale can delivery a precise refrigerant charge.
    However many of my students cannot afford for a scale.
    I would like to improve a technique that I learnt years ago still in R12 times.
    How can I charge R134 in a domestic fridge without a scale using only the manometer as a reference ?
    Could anybody describe it step by step right after the vacuum step ?
    Moises
    Apr 2011
    Russia
    140
    Re: Charge R134 without a scale
    Acrisoft, If u can mesure subcooling 5...8K I suppose it is correct. Sorry, I'm not domestic frige specialist...
    Dec 2010
    devon
    837
    easier ways i find is sweating of suction pipe with a clampmeter testing comp run amps but on a domestic you could charge on a standing pressure or and dont laugh during my junior years mothers bathroom scales they lasted bloody years but not so good on a small difference my lastest set of scales is 1 gram acuracy i think the bathroom scales depended on time of day and no battery to change
    manchester
    5,639
    use 1kg bottles and baking scales- rated for 2kg,small,cheap,and light too.
    Jul 2006
    norfolk
    737
    Split Croatia
    6,151
    Split Croatia
    6,151
    Quote Originally Posted by Acrisoft View Post
    Moises
    That is wrong technique and you cannot improve it.
    You cannot correctly charge with manometers only. You need thermometers.
    According to Danfoss service literature, you should charge to 4-7K of evaporator superheat.
    Split Croatia
    6,151
    Quote Originally Posted by AlexG View Post
    Charging to subcooling is only with TXV systems. Domestics are 99% cappilary tube and charging is done by superheat or by weight.
    Sep 2008
    Letsby Avenue
    359
    Can you afford recovery machines,do you have them ?
    “Life is like riding a bicycle. To keep your balance you must keep moving” Einstein