    Level Controll



    I have a gaugeomatic level controll on a low pressure receiver. The receiver is in low temp. NH3 service. The capacity is about 8000 lbs. of NH3. It is a pumped liquid system to four blast freezer evaporaters that are on a 3 to 1 overfeed ratio. The gaugeomatic uses mercoid switches which are no longer available. I hope within the next year to update or replace the column and the controll. I was wondering if anybody uses a Sporlan level controller? I would appreciate hearing from anyone if this idea would work or if there are problems that would rule out using a Sporlan Level Controll. Thanks C.D.


    NH3 for me

  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Level Controll

    Hi
    I have used Hansen single point level controllers for years, very reliable and parts are available if required.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Level Controll

    CHIEF DELPAC,
    Are you refering to a levelmaster control or something else?

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Level Controll

    I use danfoss level control 38 E .
    if you need information you well come.

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Level Controll

    Quote Originally Posted by RANGER1 View Post
    CHIEF DELPAC,
    Are you refering to a levelmaster control or something else?
    I'll assume its a sporlan level master which are ok as is a modulating valve.
    I could be wrong but doubt that you will get one big enough for what you want to do.

    The valve also needs to be big enough to top up vessel when you turn a freezer on for example.

    I think they are pretty basic & you will also have to instal high level/low level float switches
    with it for plant protection.

    There are a lot of more suitable controls to pick from with features to alter operating level if you like.

    Most require a level probe & controller to operate it with control valve(ideally modulating as opposed to on/off operation).


    Danfoss, Hansen, Parker

  6. #6
    Join Date
    Jul 2008
    Location
    wet coast B. C.
    Age
    76
    Posts
    122
    Rep Power
    16

    Re: Level Controll

    Thanks for the info.fellow friggies. Ranger1 Your right the sporlan valve assembly would not have enough capacity. The reason I thought of using the sporlan valve is the way the sensor is positioned. The nh3 is contaminated with refrigeration oil. I am slowly recovering the oil. Meanwhile it is causing level control problems. That why I looking at an alternitive control system. Plus the fact that it is difficult to find Mercoid switches as they are no longer availible at the parts suppliers. C.D.
    NH3 for me

  7. #7
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Level Controll

    The capacitance probes tuned for R-717 are all fooled by an oil accumulation. At low temperatures and larger vessel movements, the probe will become filmed with oil over a considerable portion of its length and that really messes with the signal.

    You need to pipe particularly the bottom connection carefully and support free draining of any oil from the liquid column to someplace else...an independent oil pot or even an extension to the liquid leg valved so that it acts like an oil pot. In some cases a 3" column is fed a trickle of refrigerant from the pumps to somewhere near the top; which will tend to keep the column itself from acting as an oil pot.

  8. #8
    Join Date
    Dec 2011
    Location
    USA
    Age
    48
    Posts
    3
    Rep Power
    0

    Re: Level Controll

    There is a new level sensor on the market that uses "TDR" technlogy not capacitance. It is unaffected by oil and is a simple cable style so you dont have to worrie about clearance above the vessel. This could be another option for you.

    AKS 4100U