    One for the HVAC Techs



    I know this is off topic, but i'm also aware a few of the members deal with heating systems aswell as A/C-Ref,
    I have a Landis & Staefa RWB9 Central heating programer installed at present (controlling heating and hot water on a baxi back boiler), the only controll it gives me is timed or manual HW/CH, Is it possible to fit a room thermostat to this controller to controll on temp rather than time, at present the heating is on untill you sweat your whatsits off then off until they shrivell,
    I have the IOM for this controller but it doesn't appear to go that far indepth,
    Thanks in advance



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: One for the HVAC Techs

    hi james,
    easyest way to turn down the return water boiler stat,
    hope that works , sedgy,

  3. #3
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: One for the HVAC Techs

    Thanks Sedgy Is that the dial next to the pilot ignition?, sorry I'm a bit green when it comes to heating

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: One for the HVAC Techs

    hi james
    ´ yes thats the one under the front of the gas fire in the middle, the above is only a short term fix you might get the room temp right , but you might have to keep adjusting as the ambiant drops , sedgy

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: One for the HVAC Techs

    Hi James

    Just wire the room stat in series with terminal 4. (CH on) at time clock or before other connections in the junction box. Possibly in airing cupboard?
    That way provided you are calling for CH via the time clock, your room stat will control your CH operation.
    Grizzly

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: One for the HVAC Techs

    Thought so I've tried that in the past but the hot water temp drops to low, the hot water I can set on a separate time schedule to the heating, and hoping to modify/upgrade the control so I can time the HW and run the CH off a tstat

  7. #7
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: One for the HVAC Techs

    Quote Originally Posted by Grizzly View Post
    Hi James

    Just wire the room stat in series with terminal 4. (CH on) at time clock or before other connections in the junction box. Possibly in airing cupboard?
    That way provided you are calling for CH via the time clock, your room stat will control your CH operation.

    Grizzly
    Sounds spot on that Grizzly do you think any mechanical tstat would do the job?

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: One for the HVAC Techs

    Any stat will do as you are only using it to switch the control supply voltage.
    I would of assumed your hot water was controlled by a tank stat?
    If not you could fit one again in series with terminal 3 (HW On).

    Some stats require a nuetral also, so that may determine where you site your connections.
    Grizzly
    Last edited by Grizzly; 08-11-2011 at 06:59 PM.

  9. #9
    Join Date
    Jun 2010
    Location
    Ireland
    Posts
    174
    Rep Power
    15

    Re: One for the HVAC Techs

    Is this going to Fan coil units or rads... it may be better to control temperature locally. (eg local thermostat for FCU or thermostatic rad valves)

  10. #10
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: One for the HVAC Techs

    It's for my boiler at home if was fcus I might have an idea
    The hw and ch are of the same stat but I can time them individually

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: One for the HVAC Techs

    OK James.
    Can you see any reason why you cannot individually control the DHW and CH?
    It would help if you know whether you have a fully pumped system or a gravity DHW pumped CH system.
    I would assume because you can time them individually that you have a fully pumped system.

    For Manuals try http://www.centralheating.co.uk/Boil...boiler-manuals

    You may find what you need.
    Good luck Grizzly

  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: One for the HVAC Techs

    james just because u work on big green things,doesnt make u a domestic heating consultant, do you have your gas safe,part p and 17th edition, otherwise get a stoker in!!!haha

  13. #13
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: One for the HVAC Techs

    James, is it a weather compensated control? Sorry for this but I 'm not sure what is meant by back boiler. I always thought it was a coil in the back of a wood fire.

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: One for the HVAC Techs

    Quote Originally Posted by MikeHolm View Post
    James, is it a weather compensated control? Sorry for this but I 'm not sure what is meant by back boiler. I always thought it was a coil in the back of a wood fire.
    Mike, a Baxi back boiler is normally a gas fired boiler fitted into the back of a normal household fireplace opening. In front of the boiler there is a radiant gas fire.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: One for the HVAC Techs

    Thanks Brian, we have no such thing over here.

    I had a look at the control and it seems you cannot get space heating unless HW is on so, given Brians description, I assume the on/off times are designed to give hot water when needed to a cylinder. There is an input for tank aquastat and/or T-stat. I doubt it is a modulating boiler which would be needed for a WC control.

    Try a t-stat but be prepared for less than ideal HW production. On the other hand, I may be totally full of s**t

  16. #16
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: One for the HVAC Techs

    Quote Originally Posted by install monkey View Post
    james just because u work on big green things,doesnt make u a domestic heating consultant, do you have your gas safe,part p and 17th edition, otherwise get a stoker in!!!haha
    Have all of the above Monkey, I was waiting for that one

  17. #17
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    251
    Rep Power
    17

    Re: One for the HVAC Techs

    A bit late but this may help you.
    http://www.gasman.fsbusiness.co.uk/f...ed_systems.htm

    To get separate time & temp control of your HW & CH I think you need to have a fully pumped system. Most common type is a Y Plan. I installed a baxi boiler in an old house of mine years ago with a 3 port flow share valve, room t'stat, tank t'stat, programmer & single pump. Like Grizzly said if you have a gravity HW system then I'm not sure how you can control the HW temp with converting to a fully pumped system.
    If in doubt read the instructions. If still in doubt follow them.