Dear Friends,
At what height the liquid receiver to be installed when all plants (compressor,motor & chiller) are at floor level. I am ***** systems installer, and now I want to start installation
of NH3 Systems. Can any body give me suggestions/data regarding NH3 systems installation and general elevation drawing data.
please mail to: kartheekus@yahoo.com
-
06-11-2011, 07:42 PM #2
Re: installation
There is no one correct answer. The receiver can be located at the same level or at a different level. When it is at a different level it is more often above the compressor(s) but it can be at a lower level. The condenser piping, the system feed and compressor oil cooling will all be factors in determining the best location for the receiver in a particular installation.
-
07-11-2011, 10:08 AM #3
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: installation
Mean thing you do and work right designing and piping- Check valve after compressor and pipe Slop to condenser and from condenser to receiver
With equalizing pipe (between receiver and condenser)
oil drain valve + sight glass+ safety valve for receiver
oil cooler should be close as much as you can to compressor
Last edited by mbc; 07-11-2011 at 10:16 AM.