    installation



    Dear Friends,
    At what height the liquid receiver to be installed when all plants (compressor,motor & chiller) are at floor level. I am ***** systems installer, and now I want to start installation
    of NH3 Systems. Can any body give me suggestions/data regarding NH3 systems installation and general elevation drawing data.
    please mail to: kartheekus@yahoo.com



  2. #2
    Join Date
    Jul 2005
    Location
    USA
    Age
    61
    Posts
    68
    Rep Power
    19

    Re: installation

    There is no one correct answer. The receiver can be located at the same level or at a different level. When it is at a different level it is more often above the compressor(s) but it can be at a lower level. The condenser piping, the system feed and compressor oil cooling will all be factors in determining the best location for the receiver in a particular installation.

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: installation

    Mean thing you do and work right designing and piping
    - Check valve after compressor and pipe Slop to condenser and from condenser to receiver
    With equalizing pipe (between receiver and condenser)
    oil drain valve + sight glass+ safety valve for receiver
    oil cooler should be close as much as you can to compressor