    Thermocold chiller alarm



    Hi.
    I have a problem with chiller AWA ANERSAVE II 2260 ZC NT SE B R407c.
    There is alarm "main fun/pump maintenance hour meter" wich I try to acknowledge but it appear again. The hour meter is 10013 hours. I can`t find any information in manual.
    Is anybody know how to acknowledge this alarm?



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Thermocold chiller alarm

    Never had an alarm from my fun pump
    Sorry couldn't resist
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Thermocold chiller alarm

    The run hour threshold is set for 10,000 hours, you need to reset the run hours.
    Unfortunately I'm not familiar with these chillers.
    What make is the controller on it??
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Thermocold chiller alarm

    The reset in the maintenance branch of the microprocessor.
    Enter with service password and reset hour counter.

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Thermocold chiller alarm

    Hi
    if it is a carel pco controller,
    you indeed need to go to the maitenence menu and reset it there.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  6. #6
    Join Date
    Aug 2011
    Location
    Ukraine
    Posts
    6
    Rep Power
    0

    Re: Thermocold chiller alarm

    Quote Originally Posted by NoNickName View Post
    The reset in the maintenance branch of the microprocessor.
    Enter with service password and reset hour counter.
    Thanks a lot.
    It is Carel pCO1 controller.
    I`ll try to find the service password. Maybe do you know?

  7. #7
    Join Date
    Aug 2011
    Location
    Ukraine
    Posts
    6
    Rep Power
    0

    Re: Thermocold chiller alarm

    The problem has solved.
    The password is 1234.
    Thanks to "stufus", "goshen" and "NoNickName"

  8. #8
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Thermocold chiller alarm

    Glad to hear it..
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!