Results 1 to 8 of 8
    Dec 2010
    Toronto, Canada
    54
    1,492
    Max compressor dome temp
    Just wondering what should be considered the maximum temp on the top of the scroll running 410A. Pick an discharge pressure of 28bar, for example.
    Aug 2009
    New Zealand
    2,556
    Re: Max compressor dome temp
    120C max ................
    Mar 2006
    Merate (LC) - Italy
    2,553
    Exactly the same as for any other compressor, somewhere in the range of 120C
    Jul 2007
    Australia
    44
    1,857
    14
    I know a lot of manufacturers (of systems, not compressors), that have a thermistor measuring there, set cut out to ~115C
    Dec 2010
    Toronto, Canada
    54
    1,492
    That's good, I put the IR gun on it and it was 60C but I was just curious.
    Mar 2006
    Merate (LC) - Italy
    2,553
    That's probably too cold.
    Jul 2007
    Australia
    44
    1,857
    14
    Yeah, 60C is a bit weird for 28bar. Hermetic recips normally run at 70C+ at lower pressures, rotaries and scrolls 80C+ at those pressures
    Dec 2010
    Toronto, Canada
    54
    1,492
    I will have to check it when I can get back in to the site. It was a quick check and I didn't look at anything else as it seemed to be pulling down well. It was off for a few hours while I did some electrical work and I had turned it on 5 min before.