Results 1 to 14 of 14
Thread: Is the answer 6K or 2K?
01-11-2011, 04:22 PM #1
OK. Guys.
Say we have a Suction Temperature of 4c and a SST of -2c.
Mathematically the answer of 4 and -2 added together is 2
However 4 to -2 is a 6c split.
So which is the answer from a superheat perspective?
01-11-2011, 04:43 PM #2
Re: Is the answer 6K or 2K?
Grizzly, +4 and -2 =6. As in 0 to +4*c sensible heat, then add the -2 to 0*c as well as it is is also sensible heat.
01-11-2011, 05:16 PM #3
- Sep 2009
- Iran
- 66
- 672
- 1
- 19
+4 -(-2)= +4+2 = +6
01-11-2011, 05:19 PM #4
Either point crosses the 0 Datum hence it`s 6 k
01-11-2011, 06:53 PM #5
Since superheat Is ^t of sst and st then it's 6C
01-11-2011, 07:18 PM #6
01-11-2011, 07:32 PM #7
sorry lads. just looking to find out how to start a new post
02-11-2011, 09:22 AM #8
01-11-2011, 07:38 PM #9
go to home select forum and then start new thread thats my method
Ps good site you have found here
01-11-2011, 07:40 PM #10
cheers quality
01-11-2011, 07:44 PM #11
hey quality, home and forum are beside each other, went in both and cant see anywhere to start new thread
01-11-2011, 07:51 PM #12
You need to select a form to post in click the forum and I normaly find the post new thread at the boottom
02-11-2011, 09:55 AM #13
Hey Grizzly
The superheat is 6.
I look at it this way - forget + and - numbers and work as if they are all 1 increments on a rule and count the difference between the two points.
Thats my story anyway.
02-11-2011, 04:55 PM #14
OK. Guys "Hands Up"!
I already knew the answer, only I watched a chap calculating a superheat value recently and he took the negative value away from the positive.
When I pointed out the correct method (as everyone else on this post!).
I though "what a good topic for the forum"!
Sadly you are all to clever.
Some interesting way of explaining all the same.
Thanks Grizzly