    SL300 defrost



    Please any help, I have thermo king Sl 300 .
    when degree becomes 5 C the unit does not run defrost
    thank you



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: SL300 defrost

    does it defrost when its at 0,what are the other temps air outlet/discharge air/coil sensor?

  3. #3
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    347
    Rep Power
    18

    Re: SL300 defrost

    the coil has to be at + 7.0 c before defrost is initiated

  4. #4
    Join Date
    Oct 2011
    Location
    Saudia Arabia
    Age
    45
    Posts
    73
    Rep Power
    13

    Re: SL300 defrost

    when I do manual defrost the fuse 3 blown.

  5. #5
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: SL300 defrost

    sounds like damper door problem ,what does fuse 3 protect,does it not say on the panel door you have opened to access fuse?

  6. #6
    Join Date
    Oct 2011
    Location
    Saudia Arabia
    Age
    45
    Posts
    73
    Rep Power
    13

    Re: SL300 defrost

    Thank you sir
    I found the fault which is shortage in damper motor 29 wire.

  7. #7
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: SL300 defrost

    your very welcome.