    Panasonic Aquarea's



    Hi all, does anyone have any experience of Panasonic's heat pumps?

    I had a visit from their rep recently and they are claiming 1 of their models the T-Cap has no loss of output down to minus 15.

    He wasn't sure how they did this though! They also claim to maintain COP's at circa 2.4 at -15 and 35 degrees flow.

    Cheers

    Jon



  2. #2
    Join Date
    Sep 2011
    Location
    France
    Posts
    5
    Rep Power
    0

    Re: Panasonic Aquarea's

    about the pansonic heat pump,first thing ,you shall be consider the compressor,
    because the pansonic compressor just fit the Asian country,which the winter temperature is not very low.
    compare to Euroep country.

  3. #3
    Join Date
    Sep 2011
    Location
    Croatia
    Posts
    5
    Rep Power
    0

    Re: Panasonic Aquarea's

    Fact is that T Cap model keep the compressor output down to -15C. This is solved by an additional EEV and sub cooler, sub-cooling principle.
    It seems an excellent product.
    Post me your email than I send you an internal scheme.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Aquarea's

    those claims are based on water temp from 30deg to 35deg out, u need 50deg for underfloor heating so ur immersion elements are gonna be on so ur total energy usage is gonna go through the roof

  5. #5
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Panasonic Aquarea's

    40C for many underfloors, Install. 35C in a good low energy house.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Aquarea's

    immersion elements are the work of the devil-a pain to change as they weld themselves to the cylinder boss and something so small consumes so much leccy! they're evil!!!

  7. #7
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Panasonic Aquarea's

    Ours are put on with a 4 bolt flange and are easy to take off if needed....ta

  8. #8
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Panasonic Aquarea's

    Quote Originally Posted by install monkey View Post
    those claims are based on water temp from 30deg to 35deg out, u need 50deg for underfloor heating so ur immersion elements are gonna be on so ur total energy usage is gonna go through the roof
    Anyone running ufh at 50C is going to need feet like a coal walking monk. No one runs ufh at fifty. Mostly between 25 and 35C depending on the weather. 40C if the installation is crap

  9. #9
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Panasonic Aquarea's

    Quote Originally Posted by Bigfreeze View Post
    Anyone running ufh at 50C is going to need feet like a coal walking monk. No one runs ufh at fifty. Mostly between 25 and 35C depending on the weather. 40C if the installation is crap
    HAHA should that not be "coal walking monkey"

    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Aquarea's

    good job u spelt that right!!! haha
    Quote Originally Posted by stufus View Post
    HAHA should that not be "coal walking monkey"

    Cheers
    Stu

  11. #11
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: Panasonic Aquarea's

    Hi Guys.
    I'm at panasonic now (go me)
    If anyone wants access to Panasonic Aquerea info
    join the proclub and download it for urself
    www.panasonicproclub.com
    click on your country's flag enter your mail and your password and other info and click send'
    it will be approved within 24hours and you can download any catalogues you need.
    All the capacities /Ratings cop/eer's etc are in the catalogues.

    Tech info is available to our customers only

    Regards

    T

  12. #12
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Panasonic Aquarea's

    I would like the tech info but the product is not sold in Canada

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Aquarea's

    dont worry mike im onto it!- lets see if i qualify- as when tech guy finds out its me who kicked off about that comp with the wrong oil in-i mught get a lifetime ban! oops haha
    Quote Originally Posted by MikeHolm View Post
    I would like the tech info but the product is not sold in Canada

  14. #14
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Panasonic Aquarea's

    sshhhh, don't say that out loud haha.

  15. #15
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Panasonic Aquarea's

    He all ready know Install Monkey I told him. While I was bagging freebies off him.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  16. #16
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Aquarea's

    could have waited for my correct compressor to land!- is that why he hasnt accepted my freind req??haha
    Quote Originally Posted by stufus View Post
    He all ready know Install Monkey I told him. While I was bagging freebies off him.
    Cheers
    Stu

  17. #17
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Panasonic Aquarea's

    NO that's because he doesn't like you.HAHA
    Quote Originally Posted by install monkey View Post
    could have waited for my correct compressor to land!- is that why he hasnt accepted my freind req??haha
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  18. #18
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Panasonic Aquarea's

    You guys suck up as much as is necessary to get the goods....haha

  19. #19
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Panasonic Aquarea's

    Not in this case Mike ,we're related .
    You know what they say "keep it in the family"
    Cheers
    Stu