    E2 device absent?



    I had a job where the 3rd rack control was loosing communication with the other 2. I thought it must have been a problem with the echelon cable but although it had the card it wasn't wired together, is this a problem with the control itself? How do they communicate together?



  2. #2
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: E2 device absent?

    Usually they are setup to communicate via ethernet, a hub would be installed in the plantroom. You can extend the delay out to 300 seconds before alarming
    ...and she said "give it to me you big fridgie"

  3. #3
    Join Date
    Jan 2009
    Location
    Sydney
    Age
    44
    Posts
    58
    Rep Power
    16

    Re: E2 device absent?

    So it was more than likely a lose RJ45 plug on the hub from the rack 3 e2?? or is this a common problem and it requires a longer alarm response time

  4. #4
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: E2 device absent?

    Can't hurt to extend the delay.
    Last edited by 750 Valve; 01-05-2012 at 06:04 AM.
    ...and she said "give it to me you big fridgie"

  5. #5
    Join Date
    Sep 2011
    Location
    USA
    Age
    45
    Posts
    84
    Rep Power
    14

    Re: E2 device absent?

    Once logged in Hit alt-t and go the peer network tab (C-5) and change the AutoDscTimeout to 999
    The ReconnectTimeout to 999 and the Peer abs Delay to 300. I have had this problem in several locations and changing these settings has cured it.