    NH3 Compressor with RWB II Plus control panel problem



    Hi every one

    I have problem with my NH3 system. Problem is when NH3 compressor run full load (I mean slide valve > 90% and motor FLA > 90) suction temp, oil temp and sep temp value is very swing and NH3 compressor stop without any error message. If compressor run with slide valve < 90% it can work very well.

    Any one have my same problem ?

    Thank you.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: NH3 Compressor with RWB II Plus control panel problem

    Just a guess, but has anyone or anything altered the working levels?
    You just may be starving the compressor or cavitateing the pump.
    When approaching 90% Slide value observe working levels, Comp operating pressures etc.
    Also check the pressure differential across pump. Is there a diff pressure switch on the Liquid pump/s?
    Does your control software not have a diagnosis page or digital input history you can interrogate?
    Logically your comp may not be at fault just an unbalance in the system.
    A bit of logical detective work may solve your issue.
    Maybe, You may find out more by manually loading system to near 90% and checking what's happening elsewhere.
    Good luck Grizzly

  3. #3
    Join Date
    Oct 2011
    Location
    Thailand
    Age
    40
    Posts
    8
    Rep Power
    0

    Re: NH3 Compressor with RWB II Plus control panel problem

    Thank you Grizzly
    I try to change every thing my control panel but still have problem.
    I think my problem is noise because I test by remove oil temp sensor to measure ambient temp by control panel

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: NH3 Compressor with RWB II Plus control panel problem

    Quote Originally Posted by angyoshin View Post
    Thank you Grizzly
    I try to change every thing my control panel but still have problem.
    I think my problem is noise because I test by remove oil temp sensor to measure ambient temp by control panel
    angyoshin,


    Have you checked/changed power supply in panel.
    If playing up can cause crazy things to happen.

  5. #5
    Join Date
    Oct 2011
    Location
    Thailand
    Age
    40
    Posts
    8
    Rep Power
    0

    Re: NH3 Compressor with RWB II Plus control panel problem

    Where possible noise come from?
    Thank you.

  6. #6
    Join Date
    Oct 2011
    Location
    Thailand
    Age
    40
    Posts
    8
    Rep Power
    0

    Re: NH3 Compressor with RWB II Plus control panel problem

    i changed power supply already.

  7. #7
    Join Date
    Oct 2011
    Location
    Thailand
    Age
    40
    Posts
    8
    Rep Power
    0

    Re: NH3 Compressor with RWB II Plus control panel problem

    I saw something in screw compressor manual.
    " The major contributor to noise is usually not directly attributable to the compressor, and most of the
    noise is likely to be generated by the oil separator, the discharge line, and the motor. These components generate noise primarily because of the pulsations of flow which are characteristic of the screw compressor. Noise generation increases when there is under- or over compression "
    I already changed motor. what i should to do with oil sep and discharge line ?

  8. #8
    Join Date
    Oct 2011
    Location
    Thailand
    Age
    40
    Posts
    8
    Rep Power
    0

    Re: NH3 Compressor with RWB II Plus control panel problem

    I saw something in screw compressor manual.
    " The major contributor to noise is usually not directly attributable to the compressor, and most of the
    noise is likely to be generated by the oil separator, the discharge line, and the motor. These components generate noise primarily because of the pulsations of flow which are characteristic of the screw compressor. Noise generation increases when there is under- or over compression "
    I already changed motor. what i should to do with oil sep and discharge line ?

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: NH3 Compressor with RWB II Plus control panel problem

    angyoshin,
    Do your sensors have screened cable & is it earthed correctly?

    The compressor should not have over/under compression if RWB calibrated & working OK.

    When was compressor last major service, maybe noise is generated from compressor.
    Last edited by RANGER1; 26-10-2011 at 10:17 AM.

  10. #10
    Join Date
    Oct 2011
    Location
    Thailand
    Age
    40
    Posts
    8
    Rep Power
    0

    Re: NH3 Compressor with RWB II Plus control panel problem

    RANGER1,
    Earthed cable of sensor is correct. Before this problem, The motor compressor was burst. After I change motor noise problem was happen.

  11. #11
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: NH3 Compressor with RWB II Plus control panel problem

    angyoshin

    Coupling & alignment might be one issue, damaged compressor the other.

    Was there a particular reason why motor blew up?

    Can you give all pressure/temp readings when compressor is running.?

    Is the noise there all the time now, or when compressor reaches a certain load?

  12. #12
    Join Date
    Oct 2011
    Location
    Thailand
    Age
    40
    Posts
    8
    Rep Power
    0

    Re: NH3 Compressor with RWB II Plus control panel problem

    RANGER1

    I test run compressor 2 time.

    No.1 Setpoint suction pressure = 3.6 bar

    Time Suct.Press. Suct.Temp. Disc.Press. Disc.Temp. Oil Press. Oil Temp. Sep.Temp. Slide Valve
    Start 3.81 bar 25 C 5.5 bar 66 C 5.86 46 76 0 %
    2 min. 3.66 16 11.85 62 11.10 42 47 55 %
    4 min. 3.66 12 11.79 76 11.03 53 64 65
    10 min. 3.65 0 11.72 78 11.16 52 77 85
    12 min. 3.64 -3 11.72 77 11.16 50 78 85

    It work can run over 1 hour without shutdown.

    No.2 Setpoint suction pressure = 3.5 bar

    Time Suct.Press. Suct.Temp. Disc.Press. Disc.Temp. Oil Press. Oil Temp. Sep.Temp. Slide Valve
    1 min. 3.68 5 11.85 71 11.03 47 74 65
    2 min. 3.65 0 11.85 75 11.03 50 74 75
    4 min. 3.68 -3 11.99 72 11.37 46 74 90

    at 4 min. noise is coming, All temp sensor value is swing, and compressor shutdown.

  13. #13
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: NH3 Compressor with RWB II Plus control panel problem

    angyoshin,
    Its not plainly obvious but it looks probable that liquid ammonia is entering compressor, especially when loaded up quicker in set pont 2.
    The oil & discharge temp drops 4 C
    The liquid ammonia in a slug entering compressor can sound pretty bad in some cases if large enough.

    I think check out levels in evaporator.

    What type of evaporator is it & how are levels controlled?

    Common causes can be oil in float or probe control column giving false levels, or leaking liquid makeup valve.

    Isolate this liquid makeup on suction accumulator if possible & resume some tests.

  14. #14
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: NH3 Compressor with RWB II Plus control panel problem

    Angyoshin,
    may not be relevent, but had a similar problem on a RWB 11 plus, stopped at full load and no indication. Eventually problem sorted out, it was one of the CT coils on incoming power to system that went crazy at full load., created a supply imbalance and tripped the system out.