    hot water coils.



    Hi chaps

    Currently in discussion with a guy regarding his hot water battery on his York package unit(supply side) . In the spec it says "hot water re-heat battery" and design is inlet 16c off 21.C

    I have told him that the battery is too small to be considered a space heater and as such he should be using his rads more.. He suggests that isn't right and it should also heat the rooms. Can anyone confirm my line of thinking



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: hot water coils.

    Richard

    Is the York a heat pump? I have a pub that has a heatpump plus a rad literally in the supply duct, as the york can't supply enough heat on its own. if it's classed as a reheat then it sounds like a close control, controlling humidity?

    al
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: hot water coils.

    Let's be honest, with an air off of 21°C it isn't going to provide much in the way of heating is it?

    That's assuming that the on temperature is at 16°C, any lower and he's lost it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: hot water coils.

    RB.
    Do you have any model No's to reference against?
    Although I tend to agree with you and Brian.
    "Silk Purse out of a Sow's ear springs to mind.
    Grizzly

  5. #5
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: hot water coils.

    just looked at the label. Seems to be straight cooling with no electric heat option fitted..DSC03440.jpg

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: hot water coils.

    A Strange one you have there RB.
    I have some old York paperwork and the best I can make out, is it is cooling only.

    With D1C meaning cooling (Mk1) model. I have assumed this from using the attached much later explanation.
    I suspect the Mk 1 is pre-pdf?
    Grizzly

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: hot water coils.

    That looks like an american made one, heater amps are listed though, are they not installed Richard?

    al
    Mostly found in the southern part of this green and pleasant land.

  8. #8
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: hot water coils.

    Quote Originally Posted by al View Post
    That looks like an american made one, heater amps are listed though, are they not installed Richard?

    al
    No difficult to see but if you look the x shows what heater is installed and the x is against none

    so it's a cooling only with no electric heaters and a small reheat hot water coil..