    Condensation levels on Air source heat pump



    we have just inherited a building to maintain which has a 18mnth old air source heat pump which is condensating heavily and water runs out and down the pathway has anyone got any ideas why it should condensate so heavily please?

    Andy



  2. #2
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Condensation levels on Air source heat pump

    Is it big enough for the room it is cooling/heating?
    Tony

  3. #3
    Join Date
    Aug 2010
    Location
    England
    Age
    53
    Posts
    77
    Rep Power
    16

    Re: Condensation levels on Air source heat pump

    in heating mode the outdoor unit becomes the cooler and so will make condensation.

    Its possible this is normal operation?

    It 'may' be short of gas in which case you. In which case you'll need a full leak test / repair / re-charge - or, if you have the time - reclaim the refrigerant and test the weight against the commissioning / nameplate charge details.

    Hope that helps?