    help!!! airdale a/c in coms romm fault is comms fault



    Hi working on 4x airedale a/c unit in a comms room they are all interlinked all have coms fault spoke to airdale (waste of time) changed main trend I Q board still no joy then changed the relay board all on airdals say so still no joy all parts changed in unit number 4

    HELP!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! server room getting hot

    Thanks
    Matt



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: help!!! airdale a/c in coms romm fault is comms fault

    Hi Shawy1

    can you link out the external run signal and run them as stand alones, for now to get out of trouble, until you solve the trend issue?

    R's chillerman
    If the World did not Suck, We would all fall off !

  3. #3
    Join Date
    Oct 2007
    Location
    Northamptonshire
    Age
    60
    Posts
    25
    Rep Power
    0

    Re: help!!! airdale a/c in coms romm fault is comms fault

    Have you got the trend display with 4 buttons on it switches,knobs sensors and alarms and an on off switch

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: help!!! airdale a/c in coms romm fault is comms fault

    hi shawy1
    airedale units used to have a auto- off - run switch in the A- H- UNIT can you turn one or 2 on run ? sedgy ,

  5. #5
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: help!!! airdale a/c in coms romm fault is comms fault

    i assume they are all run in auto if linked, usually there will be one master and all the rest will be slaves identify the master and individually run it with one airedale on at a time to find out which one is not talking to the master,once identified it should indicate in the menu what fault is causing the unit not to run and alarm causing the comms fault i.e it might be compressor alarm or return air which causes unit to stop running triggering the comms alarm ,depending on the fault you can run the unit in manual instead of auto and disable component causing the alarm without any more info thats the best i have right now gd luck mate