    Question motor problem



    Hi guys,
    I`ve got a problem with a 150kw motor that`s been working with reciprocating copressore(mycom 4wb)
    the motor burn out when compressor was running,we checked winding status,just a point of winding's burnt and it seems there is split on this point nothing more
    what is the problem?
    on the other hand we set simple star to delta method to start up our compressor,
    i suppose, onething may cause, is harsh current at starting period
    if i want to retrofitted it with an inverter or soft starter, what should i care for?(mechanicaly)in according to use reciprocating engine and etc...
    thanks



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: motor problem

    Was there along standstill? New or old motor?
    One spot is mostly a failure in the varnish.
    Why you want to use a VFD? What's the application of the motor and is it connected to a rather stable cooling system? I mean with stable, mostly the same load.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Oct 2011
    Location
    iran
    Age
    43
    Posts
    5
    Rep Power
    0

    Re: motor problem

    hey peter_1
    to some extend, motor is new,it has been working for 4000 hours
    reason is inrush current while using simple star to delta method,in this method 5 times of nominal current of the motor go through winding at starting time(of course for a while),consequently life long of motor will reduce on the other hand our electrical components have to bear this inrush current
    about compressors,they connected to rather stable cooling system,
    my concern is,likely happening this failure on other machines(we have 4 compressores mycom 4wb)
    to sum up, if i wana use soft starter or vsd to control inrush current and saving energy ,is there any mechanical limitation or etc...

    thanks

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: motor problem

    Hello
    Windings are being cooled (injection of *****) ?
    Are there enough time delay between starts of the compressor and is the number of starts / hour limited ?

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: motor problem

    dear reza
    for mycom 4wb you put 150 kw motor ? are you sure . please check it again .it is too much
    What is your suction and discharge pressure ?
    check you unload system. in start time solenoid vale should be powered( they should be open) in mycom compressor

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: motor problem

    Hi Reza.
    transition/ change over spikes can damage motor coils. If the motor is not at full speed at transition, the spike can be 10 times motor rated amps and higher. Suggest a soft start with a 5 > 7 second ramp up time. You get the advantage of low voltage start without transition spike

  7. #7
    Join Date
    Oct 2011
    Location
    iran
    Age
    43
    Posts
    5
    Rep Power
    0

    Re: motor problem

    thanks guys
    mbc,you are right compressor is 8wb instead of 4wb, suction press. 2.0/ dis. press 8 and unloader is ok(powered at starting time)
    magoo,you confirm using soft starter,although i am an electrical and know what shouid i do if i wana establish softstarter,my concern is effections of using softstarter on mechanical components (engine)
    is there any thing to warry about if i wana use soft starter?

  8. #8
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: motor problem

    hi Reza
    what is Compressor RPM.
    what is the time between on and off time?

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: motor problem

    Hi M Reza.
    no serious issues with compressor the oil differential safety has time delay. being an electrician check the motor connections between L1 and L2, not L1 to L3, L1 to L3 with increase vector shift in motor coils and increase inrush currents

  10. #10
    victoria stiles's Avatar
    victoria stiles Guest

    Re: motor problem

    Efficiency in your business operations and cost-effective solutions to your problems will give you savings and continuous production time. Electric motor repairs done by a reputable and reliable repair company can help your business run efficiently at all times.

  11. #11
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: motor problem

    Hi
    no problem fitting a soft starter to this motor.
    it is actully recomended.use a known manufacturer!!
    you should have no problem retrofiiting this motor,if you have more questiones mail me ,
    i will try to advise.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  12. #12
    Join Date
    Oct 2011
    Location
    iran
    Age
    43
    Posts
    5
    Rep Power
    0

    Re: motor problem

    Thank you goshen
    You exactly say my answer, although I have more questions, if you don’t mind
    What’s the recommended rise time in terms of using soft starter?
    And if I wana use frequency inverter, how many percent of engine’s RPM is legal, I mean until which engine RPM I can reduce speed of motor?
    By the way our engine speed is 1200 rpm
    In your suggestions you said “use a known manufacturer” , I don’t get it exactly, did you mean brand of soft starter or anything else?

    Best regards and wishes

    reza

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: motor problem

    What is rise time? Minimum speed is given by your compressor manufacturer to allow proper lubrication.
    Known manufacturer...choose a well known brand with service behind it if something goes wrong.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: motor problem

    Hi
    acceleration time is individual to each motor,the goal is to start the motor as fast as possible, while limiting inrush current, and reducing mechanichal shock,
    if you are using a vsd, then you should check with the motor maker, how low you can go, the average low speed on standard motors, is aprox 25 hz,you could probably go lower but only while monitoring the motor temp and current,
    a known brand would be my correct advise using a vsd from ABB or VACON.
    soft starters from either ABB or SOLCON or BENSHAW.
    good luck
    Last edited by goshen; 18-10-2011 at 03:27 PM.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  15. #15
    Join Date
    Oct 2011
    Location
    iran
    Age
    43
    Posts
    5
    Rep Power
    0

    Re: motor problem

    thanks guys