    Heat Pump Theory



    Air-source heat pumps

    Heat pumps use the same vapor-compression cycle as the refrigeration systems
    described above, but they have additional components that enable them to pump
    heat in either direction, such that the same equipment unit can provide cooling
    or heating. The two added components that make heat pumps fully reversible are:
    • A 4-way reversing valve, which can reverse the direction of flow
      around the refrigerant loop while maintaining the same direction of flow through
      the compressor (the next two diagrams show how this is done).
    • A bi-directional expansion valve, which is able to meter the flow of
      liquid refrigerant in either direction (for purposes of illustration, the
      diagrams below show two expansion valves and two bypass valves, but modern heat
      pumps often incorporate all of this functionality in a single valve).

    • An air-source heat pump in cooling mode acts
      identically to an air conditioner. Refrigerant vapor exits the compressor at a
      temperature in the range of 120-140°F, which is warmer than the outside air
      temperature. As a result, it spontaneously loses heat when it enters the outdoor
      coil, causing it to condense. The refrigerant leaves the condenser as a liquid,
      still under high pressure. The expansion valve lets through just as much
      refrigerant liquid as can be completely vaporized by the indoor coil. The
      pressure drop through the expansion valve vaporizes some refrigerant and lowers
      its temperature to 40-50°F. As a result, it spontaneously gains more heat, which
      vaporizes the rest of the refrigerant liquid. The low-pressure refrigerant vapor
      leaves the indoor coil, goes through a U-bend in the reversing valve, and
      returns to the compressor, where the cycle begins again.

      The reversing valve can be switched to heating mode
      such that the high-pressure output of the compressor is directed toward the
      indoor coil, which now acts as a condenser where the refrigerant gives up its
      latent heat to the room. It is then expanded in the reverse direction (compare
      with Figure 6) and vaporized in the outdoor coil, where it gains latent heat
      from the outside air. The refrigerant vapor then goes through a U-bend now on
      the other side of the reversing valve, and returns to the compressor where the
      cycle begins again.


      To summarize, the indoor and outdoor coils are where the refrigerant changes
      phase, gaining or losing latent heat through evaporating and condensing. The
      compressor drives the refrigerant around the loop and creates the high-pressure
      and high-temperature conditions that enable it to condense as a liquid. The
      expansion valve meters the flow of liquid refrigerant from the
      high-pressure/temperature side to the low-pressure/temperature side of the loop,
      such that it all will be vaporized in whichever coil is acting as the
      evaporator. The reversing valve determines which coil is on the ""high side"
      (condensing) or "low side" (evaporating) of the loop. Following the natural
      tendency of spontaneous heat flow, the high side loses heat to its surrounding
      environment, and the low side gains heat from its surrounding environment.


      An air-source heat pump can be installed either as a "packaged" unit, where
      both coils are in a weatherproof enclosure, typically mounted on flat roofs
      (Figure 8), where they supply warmed or cooled air to the rooms immediately
      below them, or as a "split" system, where the indoor coil is contained within
      the building's air handling system (Figure 9). Packaged units are more common in
      commercial and institutional buildings, while split systems are more common in
      residential applications.


      Packaged terminal heat pumps also can be installed as "through the-wall"
      units, where they are fitted into a sleeve that passes through an exterior
      building wall. These typically are noisier than rooftop packaged units, since
      the compressor and fan are located in the room; they are commonly found in
      hotels and motels.


      During the winter heating season, air-source heat pumps cease to be effective
      when the outside air temperature falls below 25-35°F. To handle such conditions,
      they are supplied with a supplemental heating system - usually electric
      resistance strips to further warm the building supply air after it leaves the
      indoor coil (Figure 9).


      During the heating season, moisture in the air outside may freeze on the
      outdoor coil if its surface temperature drops below 32°F. Therefore, when
      outside temperatures fall below about 40°F the heat pump will periodically enter
      a defrost cycle, during which the reversing valve intermittenly sends hot
      refrigerant through the outdoor coils for periods lasting anywhere from two to
      ten minutes. During a defrost cycle, the electric heater is used to warm the
      indoor supply air, but its temperature still may fall below skin temperature,
      causing a "cold blow" sensation. This is not a problem with geothermal heat pump
      units, which do not require defrost cycles even in cold weather, due to the
      stable ground loop temperature.


      Water-source heat pumps


      Water is a much more efficient heat energy transfer medium than air, due to
      its much higher specific heat. Using pumps or fans with comparable efficiencies,
      it takes four times less energy to move a given quantity of heat with water than
      with air. Furthermore, due to the higher density of water, a piping conduit
      takes up less space than an air duct with the same heat moving capacity.
      Therefore water is the preferred heat distribution medium for large, multi-story
      buildings.


      Conventional water-source heat pumps use a fossil-fuel-fired boiler as a heat
      source during the winter and an evaporative cooling tower to reject heat during
      the summer. This is sometimes referred to as a boiler/tower system; it is also
      known as a "California system", since this concept is thought to have originated
      in that state. The water loop temperature is maintained between 60 and 90°F.
      When the loop temperature falls below 60°F, the boiler adds heat, and when the
      loop temperature exceeds 90°F, the cooling tower rejects heat.


      As shown in Figure 10, there is a common water loop connected to all the heat
      pump units distributed throughout the building, which themselves can have a
      variety of configurations, including horizontal, vertical, or console. The water
      loop can be integrated with the sprinkler system to reduce cost.
    Attached Images Attached Images


    If the World did not Suck, We would all fall off !

  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Some more info to take into consideration when designing a system

    R's chillerman
    Attached Files Attached Files
    Last edited by chillerman2006; 10-10-2011 at 10:41 AM. Reason: added doc
    If the World did not Suck, We would all fall off !

  3. #3
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Evening All

    what is the main issue's with ASHP's and defrosting ?

    and what is the best way to overcome them ?

    also what is the pro's/con's of the attached type of coil ?

    R's chillerman
    Attached Images Attached Images
    If the World did not Suck, We would all fall off !

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Heat Pump Theory

    Nice summary CM, any credit to the original author would be appreciated.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Quote Originally Posted by Brian_UK View Post
    Nice summary CM, any credit to the original author would be appreciated.
    Original Post - Credit to : Geo4VA

    R's chillerman
    If the World did not Suck, We would all fall off !

  6. #6
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Heat Pump Theory

    As you have stated the heating capacity of all ASHP systems reduces as outside ambient air temps get lower – just when you need it most. As such the chosen system must be selected to meet the design heating load at the design winter conditions allowing for the capacity reduction. If sized for the design heating load at say -10c an air to air heat pump system will be oversized at any outside air temperature above the design condition – see graph below.
    Some manufacturers provide heating & cooling combination ratings or tables. These can be plotted onto a graph where the effect of the defrost cycle can be easily seen as a pronounced dip in capacity at ambient temperatures of 10 to 7°c or lower. I found an excellent document on the University of Strathclyde website which is based on actual use of Sanyo CO2 Air to water heat pump. The link below discusses aspects of the defrost cycle – bare in mind the system in question is an air to water heat pump system. Similar results / experiences can be expected for Air to Air heat pumps.


    http://www.esru.strath.ac.uk/EandE/Web_sites/10-11/ASHP_CO2/modelling_defrost.html



    As ambient air temps drop below 10°c / 50°F the outdoor coil starts to operate below freezing. As a result any airborne moisture will freeze on the outdoor coil of an Air to Air heat pump. To remove the frost the ASHP system goes into defrost mode & reverses its operation (cooling). This puts hot gas into the outdoor coil (now acting as a condenser instead of an evaporator) & melts the accumulated frost. Once the outdoor unit is defrosted the systems returns to the heating mode. The control of defrost operation is by temperature / pressure sensors &/or timers – or a combination of all. To counter the defrost operation in Air to Air systems it is normal to either shut down the indoor unit fan (cold draft prevention) or, to energise an electric resistance heater to temper the air leaving the indoor coil (now in cooling mode). These electric heaters can also be operated to supplement the heat pump heating capacity as it drops off in colder ambient temperatures. The electric heaters are normally controlled via outside ambient thermostats which will inhibit their operation until a certain ambient temperature has been reached. Multiple electric heaters and outdoor air thermostats can be used to provide staged supplemental heating. The electric heaters can also be used as an emergency source of heating should the heat pump system fail. Consideration should also be given to the amount of condensate water that will be discharged from the outdoor unit when in defrost mode. Supplemental electric heating is normally only available as an option in larger ducted single package heat pumps (rooftop type). 1 to 1 Splits & VRV/VRF type systems normally employ the cold draft prevention method when defrosting occurs & do not use any additional electric heating.


    The pictures you have attached are of USA style outdoor units i.e. square casing, “L” shaped coil with a top discharge fan. These are normally mounted at ground level or perhaps on a flat roof. However, they are not that easy to mount on cantilevered wall brackets. Most smaller capacity European style outdoor units are shallower (depth), have 1 or 2 side discharge fans and can be easily mounted on wall brackets, on the ground or on a flat roof. Multiple outdoor units can also be installed “back to back” or stacked one on top of the other if space is restricted. Some people call them condensing units or condensers which is not strictly true since they operate as a condenser in cooling mode & as an evaporator in heating mode. I prefer to use the term “Heat pump outdoor unit”. Having said, & just to confuse the issue a little, you can also get indoor mounted versions which have a ducted fan arrangement. An “indoor outdoor unit” if you will.
    If in doubt read the instructions. If still in doubt follow them.

  7. #7
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Hi Greencrocer

    Good link/info mate, cheers

    R's chillerman
    If the World did not Suck, We would all fall off !

  8. #8
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Heat Pump Theory

    CM, all the info i have accumulated about Air to water HPs, tells me that to defrost effectively keep lots space around the Evap to prevent the ice from becoming a glacier. It is not really possible with a split like a Mits or Daikin but if the coil were on an angle, drainage could be enhanced and there are some European units that do this.

    And very important is to have enough buffer water to take heat from.... to complete the defrost. I have seen some sensors that were great at detecting frost (and were used for other reasons) but i have never seen this type on refrig systems. It is another thing to research. It would be great if we could accurately sense the presence of frost and prevent a defrost coming on when not needed or to bring it on earlier if needed. I don't know how accurate, over time, current defrost mechanisms are or put another way, could we save power overall if there was more accurate detection.

    Green Grocer, in the USA and Canada, there are very few air to Water HPs. Almost all are air to air or GSHPs (which mostly heat air) and there is almost always an electric resistance back up coil in the plenum of the air handler.

  9. #9
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Hi Mike

    maybe look into 'magnehelic gauges' mate

    they were used to initiate a defrost on transport refrigeration units

    and were very effective, but not sure if still used as out of that game for long time now

    R's chillerman
    If the World did not Suck, We would all fall off !

  10. #10
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Heat Pump Theory

    A heat pump is basically no different to any other refrig system, (all have the 4 main components), how ever what is different is the massive changes in the evap and cond loads (a normal refrig system for example generally has quite a stable evap load in compassion) So you first have to manage the instability of the system.
    Most isseus arise from the application, of lack of understanding of the application, both by the client and the contractor. ASHP are not boilers, and should not be compared as a like for like application.
    Defrost is just part and parcel of air source heat pumps, there are different methods to reduce or aid the defrost issue, how ever this normally involves increased cost, or noise, again these issues should be covered with in the application/ design.
    In my opinion in semi cold climates, where whole heating is required, ASHP should only be used on slow acting underfloor heating systems, where ebbs and fall can be absorbed by the thermal mass of the concrete floor

  11. #11
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Quote Originally Posted by mad fridgie View Post
    A heat pump is basically no different to any other refrig system, (all have the 4 main components), how ever what is different is the massive changes in the evap and cond loads (a normal refrig system for example generally has quite a stable evap load in compassion) So you first have to manage the instability of the system.
    Most isseus arise from the application, of lack of understanding of the application, both by the client and the contractor. ASHP are not boilers, and should not be compared as a like for like application.
    Defrost is just part and parcel of air source heat pumps, there are different methods to reduce or aid the defrost issue, how ever this normally involves increased cost, or noise, again these issues should be covered with in the application/ design.
    In my opinion in semi cold climates, where whole heating is required, ASHP should only be used on slow acting underfloor heating systems, where ebbs and fall can be absorbed by the thermal mass of the concrete floor
    Morning MF

    From what I read of others posts and governments plans to subsidise hp's here

    I need to really get my head around these

    Would you say uk climate is suitable for ashp and if so is that just floor heating

    Or will it be good for hot water & radiator central heating

    Is there any good books/net links on the ashp's

    and water system design

    R's chillerman
    If the World did not Suck, We would all fall off !

  12. #12
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Quote Originally Posted by MikeHolm View Post
    CM, all the info i have accumulated about Air to water HPs, tells me that to defrost effectively keep lots space around the Evap to prevent the ice from becoming a glacier. It is not really possible with a split like a Mits or Daikin but if the coil were on an angle, drainage could be enhanced and there are some European units that do this.

    And very important is to have enough buffer water to take heat from.... to complete the defrost. .
    Hi Mike

    is the use of heater bars not an option

    not seen them mentioned on ashp's before

    but often see them on walk in freezers even when they have hot gas defrost

    wonder how the cost of running heater bars, balances out to useing the water

    you have heated once and will need to re-heat

    R's chillerman
    If the World did not Suck, We would all fall off !

  13. #13
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Heat Pump Theory

    1 Go back to basic refrigeration, what determines efficiency? This is fundamental.
    2 What temps do you want running around your rads?

    add 1 and 2 together what do you get.

    I am not saying that you could not use rads, but you would have teach the end user that the rads are not hot or it will not be cheap to run if he wants it hot, you can not have both.

    Your DWH, this can be looked into in a different way, and depends upon how and why it is applied.

  14. #14
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Hi MF

    1. mass flow of refrigerant & compression ratio

    2. in the buffer tank 50*c mine is set to (boiler is 60*c)

    Hmm, 1 + 2 dont add up now for sure

    To achieve water flow temps of 60*c

    Your compression ratio would have to be too wide

    Then efficiency is lost and ratio will get wider the lower the ambient falls

    See what you mean now

    R's chillerman
    If the World did not Suck, We would all fall off !

  15. #15
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Heat Pump Theory

    Quote Originally Posted by chillerman2006 View Post
    Morning MF

    From what I read of others posts and governments plans to subsidise hp's here

    I need to really get my head around these

    Would you say uk climate is suitable for ashp and if so is that just floor heating

    Or will it be good for hot water & radiator central heating

    Is there any good books/net links on the ashp's

    and water system design

    R's chillerman
    We have been installing air to air heat pumps in commecial buildings for 30 odd years. However, Air to water heat pumps in domestic buildings is a relatively new development brought about by the rise in cost of gas / electric.
    Many manufacturers offer systems for domestic application. However, key to getting the application right is matching the system as a whole to the type of house. Like most things its cheaper to install a system when a house is built. Retrofitting a system into a house is always more expensive.
    Some systems are available that generate higher water temps so these can used with existing radiators. However, in the main, to achieve the best energy efficiencies & lowest running costs HP systems with lower water temps are the better which are ideal for an underfloor heating systems.
    Its horses for courses. Start with the house. Insulate where ever possible, then select the correct Heat Pump system to suit e.g. UF system or existing rads. Add in solar etc as required.
    Best bet is to get yourself on one or two manufacturers training courses to get the low down and knowledge. Alternatively read up on anything you can get your hands on eg. http://www.daikinheating.co.uk/default.jsp

    A word of warning though. There are some real pitfalls & horror stories out there if you get it wrong. Just search this forum.
    If in doubt read the instructions. If still in doubt follow them.

  16. #16
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Heat Pump Theory

    Quote Originally Posted by chillerman2006 View Post
    Hi Mike

    maybe look into 'magnehelic gauges' mate

    they were used to initiate a defrost on transport refrigeration units

    and were very effective, but not sure if still used as out of that game for long time now

    R's chillerman
    We use "magnehelic" gauges for precise gas flow measurement when setting up commercial boilers with power burners such as Weishaupt or Riello (not natural draft), so I am familiar with some of the products.

    The main goal in the ASHP design is to increase the annual cold temp COP to help in the stability issues the Mad talks about and if solar can be included, it is possible that there could be summer power consumption could be down to 5% of normal ASHP usage. I would like to fool the system into thinking it is -5 outside when it is -15 without the use of much direct electrical consumption. If we can do that, we will be miles ahead.

  17. #17
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Heat Pump Theory

    Quote Originally Posted by chillerman2006 View Post
    Hi Mike

    is the use of heater bars not an option

    not seen them mentioned on ashp's before

    but often see them on walk in freezers even when they have hot gas defrost

    wonder how the cost of running heater bars, balances out to useing the water

    you have heated once and will need to re-heat

    R's chillerman
    Heater bars would be my last choice as they are direct resistance (if I am thinking of the same thing as you are).

  18. #18
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Hi Mike

    you certainly got an interesting project mate and can see your gradually overcoming the obsticles, if I am following you here, as long as you got sun, regardless of ambient you can increase suction pressure foc and following all your (everyones) posts here, good insulation coupled to underfloor heating, am starting to see the theory coming together

    If you can get 10*c heat increase in the evap enclosure, that would be good here where I am as rarely drops below...... -5*c and normaly above freezing, the bit that I am at 35*c is where I place water off, but then I am looking at it with water flow rates for heat rejection(chillers) not heat recovery

    What temperature are you aiming for ? and I presume the more passes the better allowing for stratification in the tank to gradually take place and cop to remain high as long as possible ?

    R's chillerman
    Last edited by chillerman2006; 18-10-2011 at 03:25 PM. Reason: high not low
    If the World did not Suck, We would all fall off !

  19. #19
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Quote Originally Posted by Greengrocer View Post
    We have been installing air to air heat pumps in commecial buildings for 30 odd years. However, Air to water heat pumps in domestic buildings is a relatively new development brought about by the rise in cost of gas / electric.
    Many manufacturers offer systems for domestic application. However, key to getting the application right is matching the system as a whole to the type of house. Like most things its cheaper to install a system when a house is built. Retrofitting a system into a house is always more expensive.
    Some systems are available that generate higher water temps so these can used with existing radiators. However, in the main, to achieve the best energy efficiencies & lowest running costs HP systems with lower water temps are the better which are ideal for an underfloor heating systems.
    Its horses for courses. Start with the house. Insulate where ever possible, then select the correct Heat Pump system to suit e.g. UF system or existing rads. Add in solar etc as required.
    Best bet is to get yourself on one or two manufacturers training courses to get the low down and knowledge. Alternatively read up on anything you can get your hands on eg. http://www.daikinheating.co.uk/default.jsp

    A word of warning though. There are some real pitfalls & horror stories out there if you get it wrong. Just search this forum.
    Hi Greencrocer

    thanks for info and link again mate, I will keep chipping away at this for probaly the next year prior to taking a course, as need to understand enough to make the most of a course

    R's chillerman
    If the World did not Suck, We would all fall off !

  20. #20
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Heat Pump Theory

    Quote Originally Posted by MikeHolm View Post
    Heater bars would be my last choice as they are direct resistance (if I am thinking of the same thing as you are).
    Hi Mike

    yes same mate, direct resistance

    R's chillerman
    If the World did not Suck, We would all fall off !

  21. #21
    Join Date
    Sep 2005
    Location
    India
    Age
    49
    Posts
    30
    Rep Power
    0

    Re: Heat Pump Theory

    We are the manufacturer of ASHP to water. For defrosting we use a combination of Temp controller to measure ambient temp, cyclic timer and solenoid valve.
    As we know there will be temp drop of 5-8 deg. C in air across evaporator, as soon as the ambient temp reaches at 7-8 deg. C, our temp. controller activates the solenoid valve so that compressor discharge, instead of Condenser diverts to Evaporator for 3-5 minutes. The cyclic timer is used to determine the timing of Compressor Discharge Diversion". If the temperature is continuously below 8 deg. C, then the cyclic timer makes this diversion after 15 to 30 min i.e. SET time based on the location.
    We found it very effective, low energy consumption than electric heated bars.
    We have installed this mechanism in 41 systems, having capacities (input) from 1 TR to 25 TR compressor at a single location.