    R410A and R22 Compressor



    Hello.

    Does anyone know if there is a way to use R410A or any other available (widely available enough) non-ozone depleting refrigerant in a typical R22 9,000 BTU compressor?

    I'm not sure about propane because there seems to be a safety issue, and refrigeration store don't sell it here.

    I am new here and just learning about air conditioning and refrigeration, and am unfortunately experiencing difficulty finding the information that I need.

    Thank you for your time.



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: R410A and R22 Compressor

    Maybe try contact the compressor manufacturer and see what they recommend?
    I've heard a few drop in refrigerants, but all seem to contain HCs from memory. And of course no point in using anything that the compressor manufacturer recommends against. But R410a definitely is a no.

  3. #3
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: R410A and R22 Compressor

    Hi Kompulsa

    as 'Paul' said

    go for drop in replacement as other refigerants can be ok with compressor but not system design

    and again agree deffo not R410a

    I have got away with using R404a txv power assembly's on some R22 chiller units

    But R404a will not work with the mineral oil in a R22 system

    R's chillerman
    If the World did not Suck, We would all fall off !

  4. #4
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    15

    Re: R410A and R22 Compressor

    Compulsa, as Paul and Chillerman said ask manufacturer. But i am sure manufacturer sais NO for R410A. Look at the difference in pressures of R22 and R410A. Even if you replace oil you can destroy your R22 compressor by high pressure. If you dont like R22 replace oil for POE and use R407C. I did it...

  5. #5
    wreich66's Avatar
    wreich66 Guest

    Re: R410A and R22 Compressor

    Kompulsa, the other guys are spot on. 407C is a great alternative to R22 with similar pressures. Temperature and pressure will be way to high if you run 410A. Compressor will go out on thermal overload or break. Make sure you stay away from propane or any other hydrocarbons with a hermetic compressor!

  6. #6
    Join Date
    Dec 2009
    Location
    Ontario
    Age
    44
    Posts
    7
    Rep Power
    0

    Re: R410A and R22 Compressor

    not that i would ever need to use it, but for curiousity sake; why not use a hydrocarbon with a hermetic compressor, because of the possibility of a short internally?

    thanks. Ernie.

  7. #7
    Join Date
    Jan 2009
    Location
    Canary Islands
    Age
    74
    Posts
    144
    Rep Power
    16

    Re: R410A and R22 Compressor

    To answer the original question.....
    Of the common a/c refrigerants, R407c or R410a are not compatible with the mineral oil that will be in a (designed for) R22 compressor. However, R422d, R424a R427a (there are others) are 'drop-in' refrigerants and compatible with mineral and poe oils.
    We use R424a as a substitute for R22 with absolutely no problems, indeed have topped-up a 22 system with 424 (after having identified and repaired the leak - of course!). 18 months on and no problems.
    Of course the R42* series are expensive. Here in Tenerife approximately twice the price of R410a!
    Will post our experiences of the Spanish regs imposed 4 July 2011 another time.
    Regards to all, Graham