    How to find proper compressor?
    I have a walk in freezer it is not cooling enough at all. The condition is as follows.
    Designed box temp.: -5F
    Actual box temp.: 14F
    Box size: 6 x 6 x 6.4ft
    condensing unit : unknown.
    compressor : Tecumseh AJ2425A
    TXV : Sporlan GFE-1/2-ZP
    Unit cooler: Trenton Low profile 1 fan unit, unknown model #.
    Gas : R414b
    I think the compressor is not enough capacity to cool down the box design temp. So I am going to change the compressor to more proper one of R404a compressor but I don't know what size of compressor it needs. Of course I have to change the TXV too. I imagine original compressor was more larger capacity, but someone has changed the compressor only before w/ some reason. The receiver outlet tube size of condensing unit is 3/8" and suction tube is app. 5/8".
    I think the compressor has to be of at least 3500 btu/hr (-20F evap temp) capa. for the size of the freezer box. The owner want to change the compressor only due to the cost.
    The question is if I increase the capacity of compressor only to 3500 btu/hr (-20F evap temp) one . it will be ok with the condensing unit?
    Apr 2006
    55
    1,908
    30
    Re: How to find proper compressor?
    Hi jayryu
    sorry to say your method will not work
    to design a system you have to calculate your heat removal requirement first
    that will then enable you to specify an evaporator
    then next you match up condensor/compressor/txv to that evap
    increasing the size of a compressor in a already designed/balanced system
    will just cause problems that can only be corrected by going back to designed spec compressor
    R's chillerman
    If the World did not Suck, We would all fall off !
    Jun 2008
    Canada
    72
    Thank you chillerman2006,
    I have calculated the heat load of the wif box about 3800 btu/hr.
    AT present, I think the system is obviously unbalanced. The compressor looks not original. Evaporator capacity looks 3800 btu(at -20F), and compressor is only 2500 btu/hr(at -10F evap temp.). Therefore I think the original compressor has been changed to this present compressor w/ some reason. I am doing my best to reduce the cost to minimum. With this condensing unit, is it possible to change the compressor only to R404, low temp abt. 3600 btu/hr compressor?
    Apr 2006
    55
    1,908
    30
    Hi Jayryu
    from my minimal understanding of design
    your compressor needs to be a match for the evaporator or very slightly oversized
    maybe someone can correct me but I would be looking at a compressor of 3800btu
    hopefully your txv is sized correctly for mass flow and only the power assembly needs changing for R404a
    R's chillerman
    Sep 2003
    ISRAEL
    72
    4,248
    By using a bigger compressor you will not solve anything. All the parts have to fit each other.
    after you have calculated the heat load, you need the right capacity evaporator,the refrigerant you want to use, the right size TXV, the right size condensing units.
    No cutting corners in refrigeration, only in carpentery, choose your side.
    Jul 2010
    NTH.QLD Australia
    1,730
    32
    Jayryu, How do you know compressor is not origional?
    Jun 2008
    Canada
    72
    The compressor model is AJ2425A. Condensing unit with that size of compressor has to have 1/4" liquid line, but the liquid line size is 3/8". That means the condensing units is more than 3500 btu/hr capacity minimum with R-12 system. One more thing, TXV valve size at present is 1/2 nominal ton. But with that size of compressor, TXV has to be 1/4 nominal tonnage if the compressor is original. Therefore I imagine the original compressor was at least 3500 btu capa. and it was replaced with this small size compressor by someone with some reason.
    This condensing unit works properly as SH -- 23 F( at compressor suction), SC -- abt. 14 F.
    But the best box cool down temp. is 14F.
    Jun 2008
    Canada
    72
    Hi Chemi-Cool,
    I appreciate your post, but I myself knows very basic. I can choose easy way, but I try my very best for my customer always. Replacing evaporator, c/u is the most easiest thing and profitable. But I do my best to save the money for my customers anytime possible. At this matter if I had enough data of Evaporator, condensing unit, etc. of course I have already changed the compressor only, it saves a lot of money for the customer.
    But this time, there were no data at all and only my experience and guesses. Therefore I wanted every recommendation of you gentlmen. Thanks again.
    Split Croatia
    57
    6,151
    36
    You could take measurements of evaporator dimensions, number of pipe rows, number of pipes and pipe diameters, fins spacing. Also, size of fan and number of blades, blade angles, fan rpm. Also, picture taken by digital camera will help to recognise what model of evaporator you have.
    That will give us full picture of evaporator and we could then tell if evaporator is of right capacity.
    Same goes for condenser.
    By my quick calculation you need at least 5000 btu of capacity if your insulation thickness is 4" (floor, roof, walls) and light loading conditions with 18 hours of run time and ambient of 90°F.
    Therefore changing compressor to 3500 btu will not help even if evaporator and condenser are matching to that compressor. Compressor will be running non-stop and maybe never reach -5°F at ambient near 90°F.
    Jul 2010
    NTH.QLD Australia
    1,730
    32
    Jayryu, from me quick search, the AJ2425A, or Z, has a capacity at -23.3 C of 2450 BTU. Only have current lists on compressor capacity handy at the moment and some of those are rated for only -15C. I always try and get as much history of machinery i work on from the customer so as to figure out the kinks, so to speak. Do you know if this freezer was getting to temperature, with current compressor on board any time before you started on this job?..Mike.
    Jun 2008
    Canada
    72
    The customer bought the restaurant only recently and is renovating the lot. He does not know any history. Even if he can contact the former owner, he would not get honest answer as a matter of fact.
    Jun 2008
    Canada
    72
    I have replaced condensing unit & TXV. Condensing unit is 3800 btu unit at -20F evap temp. Everything is working fine. Thanks everybody.