  1. #51
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP



    Quote Originally Posted by Bigfreeze View Post
    I think Mikes issues lied with the cost of drilling in Canada, local regulations and drillers just being difficult to work with in general.

    If you give me the insulation spec and dimensions for the house I'll do a heat calc for you and work out a borehole depth and HP size
    Yea, BF is right, all of the above but also, where I work the houses can have quite a small area for drilling and our code is that we must design for -20C even tho we rarely see it. The average house here would need 4-5 boreholes 200-250ft deep to meet the loads and the holes MUST be at least 10ft apart to keep from freezing the ground.



  2. #52
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Quote Originally Posted by MikeHolm View Post
    Yea, BF is right, all of the above but also, where I work the houses can have quite a small area for drilling and our code is that we must design for -20C even tho we rarely see it. The average house here would need 4-5 boreholes 200-250ft deep to meet the loads and the holes MUST be at least 10ft apart to keep from freezing the ground.
    Hi Mike

    wow! when BF first mentioned borehole to me, my first thought was I wonder if I can dig that myself and save some money.... I would not have needed any heating for the house, I would have finished my days out digging my life away, haha

    R's chillerman
    If the World did not Suck, We would all fall off !

  3. #53
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Much easier where the heat loads are lower, like most of the UK. Some areas here have design temps of -35 to -40 so it is a bit of a chore to design the system but that is not the norm.

    Seriously, for your system, right now you can adjust things to lower the bill. How big is the house and what is the boiler input?

  4. #54
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Quote Originally Posted by MikeHolm View Post
    CM, get rid of your vented system(it is really old school), just cap it then put in an expansion tank on the return side of the boiler and you will have a more stable system and no risk of corrosion in those steel rads of yours.
    Hi Mike

    missed this post earlier, mate

    I have an expansion tank in the tank cupboard along with the pump

    am presuming now its an expansion tank

    if it is, can I just cap off the overflow/prv outlet ?

    R's chillerman
    Attached Images Attached Images
    If the World did not Suck, We would all fall off !

  5. #55
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Now you have me a bit confused. I think that what I am looking at is a DHW cylinder, pump and an expansion tank. In some places there is a check valve (non return valve I think you call it) on the cold water coming in and to take up expansion when the tank heats up the exp tank must be there. But this may have nothing to do with space heating (not enough info).

    Where is the boiler? Is there a heat exchanger in the tank?

  6. #56
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi Mike

    house is three storeys, tank in picture above is on 1st floor, boiler is on ground floor, dimensions are 6x8 metres (per floor) could not find any info on bolier apart from model, as on attached pic...this was a right bogit & scarper install by one of her relatives, who dare not come round since and face me, wrecked the house, holes left in ceiling, ran skill saw along next to joists, then screwed 2x2 timber to joists and relayed floor, carpet deteriated along the gaps left behind, [deep breath] but still better than what was here which was gravity fed system with tank on first floor, very little flow to 2nd floor!

    I think there is heat exchanger in tank, as bolier is not a combi boiler

    R's chillerman
    Attached Images Attached Images
    If the World did not Suck, We would all fall off !

  7. #57
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    OK, that boiler is a Baxi product with a max output of 15kw. IF your house is enclosed on two sides and the windows and air infiltration are reasonable, it should have no trouble keeping up with the demand. I see from the pic that there is a 3 way valve that divides between the heating the tank and the rads. I assume that the valve is normally set to heating.

    Was the tank there before or or it new? Often tanks like that have a small HX and the boiler must stay on quite a while and at high temp to keep it heated. It is also possible that the setup syphons heat from the tank to the rads and the tank must call for heat more often. That part is just conjecture in regards to your system.

    Why did the service guy turn up the gas pressure or was it just the water pressure?

  8. #58
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi Mike

    the water tank was installed with boiler and yes it heats house no problem, in the winter I leave heating on 24/7 and just control temp via rad stats, one rad in hallway groundfloor has no rad stat, main wall stat normally set to, 21-25*c....yes inclosed 2 sides and new double glazing windows and doors, both heating and hot water work/heat up quickly

    I called for service due to high gas bills this year and he adjusted the water pressure but left filler loop connected afterwards and this was now letting by, increasing system to mains water pressure, and when boiler came on, lifted prv and she just watched hot water come out of overflow for months, before I spotted algae on rear wall of house

    Even though it works ok, I want to rip it out and start again at some point and I dont want any tube connections under the floor as want to lay new floor boards through out and dont want them lifted for anything once laid, I also have water tank in the loft/attic that I want shot of, which currently gravity feeds cold water to hot water tank/bathroom and toilets...the kitchen and boiler are all thats on mains water

    need to work out what would be best to install here and get it all fitted next summer

    R;s chillerman
    If the World did not Suck, We would all fall off !

  9. #59
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    191
    Rep Power
    20

    Re: My first self made EVAP

    what;s your boiler temperature set to ?

    anything more than 55'C and the boiler stops being a condensing boiler and just acts as a normal boiler
    (return water is too hot for the hot moisture to condense on) and efficiency plummets (lower than a normal boiler)

    also, make sure that stat on your hot water tank is set lower than the boiler temperature !


    when my parents had there new heating installed, the boiler was set to 60'c, but the hot water tank to 80'C... so the tank always called for more heat, but the boiler could never take it over 60'c....

    the boiler ran 27/7 trying to heat the hot water tank up.... I knocked it down to 50'C and now the boiler hardly ever runs ! :-)


    can you take some more photos of the tank and plumbing there ?


    by the look of it (and some of it is guess work here because I can't see everything)

    you have a system boiler - so it just heats the same water pumping it round and round...

    the 3 way valve picks where the water coming out of the boiler goes... it'll either go through the hot water tank heat exchanger or through the radiators.... there'll normally be a pressure valve here too so if there's a flow restriction etc.. some of the water will bypass from just before the valve and back down the return to the boiler (some valves can even split the flow between the tank/radiators)

    if you have mains pressure hot water (looks like you do) the cold water into the bottom of your tank will come straight from the water main, with a non return valve and your expansion tank connected just after it (to take the pressure as the water heats and expands)

    but... it looks a bit like your expansion tank is fitted to the heating water... I've never seen a system like that before.... but I'm not a heating engineer so it could be normal... you only need a small expansion tank here... and most boilers have one internally...

  10. #60
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi Mike

    what temp can I take tank down to ?

    boiler is mains fed for (manual) top up only, tank is gravity fed from water tank in loft

    could be half my problem is 3 storey town house,

    when its comfortable on ground floor, 1st floor is hot and top floor baking!

    thinking of ducting top floor to ground in attempt to balance it out

    R's chillerman
    Attached Images Attached Images
    • File Type: jpg 1.jpg (91.1 KB, 11 views)
    • File Type: jpg 3.jpg (91.8 KB, 8 views)
    Last edited by chillerman2006; 12-10-2011 at 04:09 PM.
    If the World did not Suck, We would all fall off !

  11. #61
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    There is a lot here.
    First,if the boiler is set to 50-52 and the tank is set to 50, it won't turn off. Either increase the boiler temp or decrease the tank temp at least 5 deg.

    Second, what is the mains pressure? It needs to be 2.5- 3 bar for the DHW to work properly and the heating for a 3 story house needs to be minimum of 1.2bar. It is possible that the mains is low and the exp tank is there for that but i doubt it. One problem is that you appear to have both an bladder type exp tank (which is turned upside down and should not be) and a old style fill tank on the top floor.

    As I said before, get rid of the top one and cap the line. How many rads do you have in the house? I suspect you need a bit bigger exp tank than the white one, probably 25L or so as there is none in the boiler. You will need a pressure reducing valve from the cold water to the heating loop (placed beside the exp tank and all this should be on the suction side of the pump).

    Condensing boilers do need to run at lower temps then non condensing but unless your natural gas is different than ours (which I doubt), condensing will start at 60C return water temp and gets better as you go down in temp. Even if you run the boiler at 80C you still will not get worse than the non condensing boiler but you are wasting energy.

  12. #62
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    EXP tank in pic is on the wrong side of the pump. Turn down the stats on the top floor (DUH, I'm sure you have done that already.) I assume the boiler is not weather compensated>

    Off to work now so i will blab on more when i get home.

    Cheers

  13. #63
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Quote Originally Posted by MikeHolm View Post
    There is a lot here.
    First,if the boiler is set to 50-52 and the tank is set to 50, it won't turn off. Either increase the boiler temp or decrease the tank temp at least 5 deg.

    Second, what is the mains pressure? It needs to be 2.5- 3 bar for the DHW to work properly and the heating for a 3 story house needs to be minimum of 1.2bar. It is possible that the mains is low and the exp tank is there for that but i doubt it. One problem is that you appear to have both an bladder type exp tank (which is turned upside down and should not be) and a old style fill tank on the top floor.

    As I said before, get rid of the top one and cap the line. How many rads do you have in the house? I suspect you need a bit bigger exp tank than the white one, probably 25L or so as there is none in the boiler. You will need a pressure reducing valve from the cold water to the heating loop (placed beside the exp tank and all this should be on the suction side of the pump).

    Condensing boilers do need to run at lower temps then non condensing but unless your natural gas is different than ours (which I doubt), condensing will start at 60C return water temp and gets better as you go down in temp. Even if you run the boiler at 80C you still will not get worse than the non condensing boiler but you are wasting energy.
    Hi Mike

    turned boiler off and used some hot water, static pressure is 1.4bar

    tank set to 50*c, turned on boiler

    and cut out at flow 72*c and return 61*c with pressure @ 1.8bar

    Temps taken with strap probes 10cm from boiler and pressure gauge is on return

    mains water pressure here is over 5bar

    am pretty sure tank fill comes from loft/attic cold water tank, which gravity feeds from roughly 6 metres above and feeds into rear/bottom of HW tank

    there are 7 rads (6 x rad stats, hallway ground floor no rad stat, runs off wall stat on first floor)

    top floor rad stats now set to 3 of 5 and blob silicone so can check they not been fiddling with them

    and will get the DHW set up on mains with pressure reducing valve and do away with loft tank and move expansion tank to other side of pump, this summer as I can send them on holiday then whilst I get it all sorted

    for now turning boiler down to 55*c and tank to 45*c, should see some improvement ?

    you say exp tank is upside down, is this an issue ?
    thanx mate

    R's chillerman


    Quote Originally Posted by MikeHolm View Post
    EXP tank in pic is on the wrong side of the pump. Turn down the stats on the top floor (DUH, I'm sure you have done that already.) I assume the boiler is not weather compensated>

    Off to work now so i will blab on more when i get home.

    Cheers
    ps: boiler temp adjustment is useful nice of them to mark out temps
    Attached Images Attached Images
    Last edited by chillerman2006; 12-10-2011 at 03:59 PM. Reason: added pic
    If the World did not Suck, We would all fall off !

  14. #64
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: My first self made EVAP

    You can't remove the header tank without replacing it with something else. Its against regs for mains water to be sent to toilets etc. There must be a break tank installed. Also you've have no water if mains goes.

    Don't know why you have an expansion tank at all. I can see no purpose on an open system with a gravity feed tank supplying the pressure. Although it is possible that the boiler/rads circuit is pressurised.

    The tank will have one coil which the boiler water runs through and heats the tank. I'd imagine the 3 way valve is to divert flow either to rads or tank depending on demand.
    Last edited by Bigfreeze; 12-10-2011 at 07:41 PM.

  15. #65
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Quote Originally Posted by Bigfreeze View Post
    You can't remove the header tank without replacing it with something else. Its against regs for mains water to be sent to toilets etc. There must be a break tank installed. Also you've have no water if mains goes.

    Don't know why you have an expansion tank at all. I can see no purpose on an open system with a gravity feed tank supplying the pressure.

    The tank will have one coil which the boiler water runs through and heats the tank. I'd imagine the 3 way valve is to divert flow either to rads or tank depending on demand.
    Evening BF

    header tank will have to remain then, cheers

    the expansion tank, would this be for the heating system

    from what I can make of this, there are two seperated circuits

    the hot water which is gravity fed and

    the heating circuit which is sealed? and mains fed

    without expansion tank, how is system pressure controlled ?

    R's chillerman
    If the World did not Suck, We would all fall off !

  16. #66
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: My first self made EVAP

    Hi CM,

    The water is gravity fed to the bottom of the hot water tank which pushes the hot water out the top of the tank and off to your taps. The boiler circuit is closed loop, circulating from the boiler to the rads or through coil in tank depending on demand. Pressure of 1-1.5 bar is fine here as the water going up will be balanced by the water on way down. The pressurisation is mainly to keep air out of the system, for rad performance and corrosion issues. The exp tank, as Mike said, should be tee'd in on the inlet side of the pump. I don't think any of this would affect your gas bills though

  17. #67
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi BF

    thanx for the step by step mate, seems the setup is not as bad as first thought then, apart from need to move the exp tank and bring my temps down a bit, cheers

    R's chillerman
    If the World did not Suck, We would all fall off !

  18. #68
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: My first self made EVAP

    No its fine, just messy looking. Had a look at the pics there. Can't make out if the arrow on the pump is pointing down or up. I assume its up, so then the exp tank would be better on otherside but not the end of the world either.

  19. #69
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Quote Originally Posted by chillerman2006 View Post
    Hi BF

    thanx for the step by step mate, seems the setup is not as bad as first thought then, apart from need to move the exp tank and bring my temps down a bit, cheers

    R's chillerman
    Guys, we are talking about the same thing. I was pointing out that there is no need for an expansion tank and a gravity feed/expansion tank so get rid of one or the other.

    The water feed i was talking about drops mains down to 1bar and is adjustable. Add an approved check valve and you won't lose your boiler water if the mains go down. Every boiler system in North america works this way. Use a proper sized exp tank and you can keep the water oxygen free for years so your rads will last a long time and there will be no need to bleed rads every year as some people need to do.

  20. #70
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Quote Originally Posted by Bigfreeze View Post
    No its fine, just messy looking. Had a look at the pics there. Can't make out if the arrow on the pump is pointing down or up. I assume its up, so then the exp tank would be better on otherside but not the end of the world either.
    The problem with exp tanks with the port up is that sometimes air gets lodged in there and if the bladder doesn't stay wet, it doesn't last as long. That is why i keep them the other way around.

  21. #71
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Thanx Gents

    will get a larger exp tank and mount up the other way and other side of pump, as there was loads of air in the system, pipes hammering for weeks, drove me mad, I presume I will get two tell tale signs if the bladder goes prior to moving/changing it, one being a pressure drop and two the outer wall will get hot to the touch, currently cool, all the info appreciated cheers

    R's chillerman
    If the World did not Suck, We would all fall off !

  22. #72
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: My first self made EVAP

    Quote Originally Posted by MikeHolm View Post
    Guys, we are talking about the same thing. I was pointing out that there is no need for an expansion tank and a gravity feed/expansion tank so get rid of one or the other.

    The water feed i was talking about drops mains down to 1bar and is adjustable. Add an approved check valve and you won't lose your boiler water if the mains go down. Every boiler system in North america works this way. Use a proper sized exp tank and you can keep the water oxygen free for years so your rads will last a long time and there will be no need to bleed rads every year as some people need to do.
    You need the header tank in this situation Mike as we have different regs in the UK and Ireland regarding mains water,than the US and Europe do

  23. #73
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    BF, you have said that mains water is not allowed to go to toilets...what water goes to the toilets?

    is the drawing below not allowed in the UK and Ireland?

    boiler and tank drawing.jpg

  24. #74
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: My first self made EVAP

    No, afaik you need a break tank. Basicly a tank 200-300L where the mains water is collected and then distributed to taps, showers, toilets etc by either gravity feed or pump. You only run mains to the kitchen sink (drinking water) and an outside tap.

  25. #75
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    The above is the most common set up here. I wonder if it is only historical reasons for not allowing other methods because we are as paranoid about legionnaires and other issues as Europe and the UK are. Using your method, the volume of water per shower may be less but no one cared about that 50 years ago so I cannot see the benefit of the system.

  26. #76
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi MIke

    Maybe it was just in case the mains water supply was lost, when I was kid I remember this was a quite common occurance...those without water tanks, knocking on neighbours for a kettle full for some rosey lea

    Cant remember the last time this happened as so long ago, but if thats due to where I now live (modern supply network, old addresses in London was victorian, I think....I know the sewers still are) and newer installations are less prone to leaks or if it was a case of supply issues back then, no idea

    R's chillerman
    If the World did not Suck, We would all fall off !

  27. #77
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Morning CM. Are you doing this on a mobile while pissing away your employers time? LOL Or is it lunch time and you are in the pub.

    You are probably right about the historical stuff but I would think it would change by now. One benefit of the the lower pressure from the tank is less water consumption from showers. Toilets will fill slow tho. How do those toilets that work on 3 bar pressure to flush work in the UK?

  28. #78
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi Mike

    back on track for you, as we swayed off subject slightly,

    R's chillerman

    Quote Originally Posted by MikeHolm View Post
    It's my first EVAP, just a fan, TXV, sensors and coil. Everything else is indoors but i won't show that to you yet as the wiring sucks and I have to clean it up Take note BF.
    Quote Originally Posted by chillerman2006 View Post
    Hi Mike

    nice shiny black mate looks pretty and neat job

    picture is decieving - is there an opening at the bottom for air intake

    at first glanc it looked like it was sitting on the ground and balancing

    on 6 inches of earth. haha my eyes, must be age catching me up

    R's Chillerman
    Quote Originally Posted by MikeHolm View Post
    It is off the ground by about 24" for drainage and it's British racing green, being a 60's BRM and Lotus fan, I thought that appropriate. Quiet as a church mouse. I was wondering if anyone would say anything....except for mumbling "what a pile of shyte"
    Quote Originally Posted by chillerman2006 View Post
    now you say it, my eyes can see its brg

    whats 'brm' ?

    and now my turn for the questions, with a cooling system you select the evap for required work

    then add compressor/condensor/txv to match

    How do you design a heat pump ?

    Do you start with the condensor and then match components ?

    R's chillerman
    Quote Originally Posted by chilliwilly View Post
    Did you make the coil yourself or did you buy it?
    Quote Originally Posted by MikeHolm View Post
    BRM was British Racing Motors who made some great racers in the 50s and 60s and Lotus is....well....Lotus.

    I had a comp from a 12kw (give or take) heat pump that someone smashed up badly. it is a ZP40 and the only other good thing in it was the TXV and a couple of pressure switches. That was my starting point and the house is not too large so it may be a reasonable fit.

    I used the least scientific method available to determine the coil, I added up the tubing surface area of the busted up wrap around (standard north american type) and the aluminum fin surface area and the volume of the tubing and using all the discussions with all you guys and a s**tload of research, I drew up the coil and had it made by a local establishment. I'll look for a coil end photo to post but I basically wanted a horizontal coil which appears to be the best for defrosting. The coil is 30" by 60", 4 row, 2 evenly split runs.

    It will still take me a long time to get used to things like coolpacks so I didn't rely on it for anything although I tried. I don't know enough yet to use it with any certainty.

    I picked 40C as my target temp for the buffer (450L, UFH and no dhw). I used the SWEP design software for the condenser (which I think may be a little bit small, but we will see as the year goes on) and I have bought lots of Hx from them before so I like the product. I cheated in that I didn't have to size a TXV (assuming my evap is sized right) so we will have to see how it runs, so far so good.

    Real seat of the pants flying.
    Quote Originally Posted by chillerman2006 View Post
    Hi Mike

    your method appears logical mate

    you have evap/comp/txv already matched, replaced evap with equal volume evap

    then matched condensor to system, an half educated thought would be on setup

    you will need to balance the system by air flow across evap and suction superheat/mass flow

    to get your desired condensor temp but taking into account compressor protection

    nice one mate, design is way beyond me now but maybe one day


    R's chillerman
    Quote Originally Posted by MikeHolm View Post
    Thanks CM, I know my liquid fluid flow quite well but I'm still a novice in the "art" of refrigeration so it is actually a big step for me (old hat for many here I suspect)
    Quote Originally Posted by Bigfreeze View Post
    Nicely done Mike. You'll have good defrost draining from that design and protection from snow. Also the height of the ground and lack of legs makes a back build of ice also impossible. Good work mate.

    If only I could progress my own projects as quickly
    Quote Originally Posted by mad fridgie View Post
    Where is the fan, is this induced draft or forced draft.?
    The does the air blow up out of the evap or down out of the evap?
    Quote Originally Posted by mikeref View Post
    Mike, this now explains why you are difficult to find. Goober, just keep that office chair polished and think about the fun you are missing out on by not being on the tools ..Mike.
    Quote Originally Posted by MikeHolm View Post
    Attachment 7900
    It had just finished raining so it looks wet. it is an updraft VSD unit. I haven't gotten to insulating the piping when i took the pic but it's done now.
    Quote Originally Posted by MikeHolm View Post
    All this will put me in the poor house for sure but it is great fun. I love the challenge.
    Quote Originally Posted by mad fridgie View Post
    Lets look at this as a purist
    We do we want for efficiency, the highest possible air entering temperature, and air that is easiest to move.
    So ,looking at the picture we can see that we are in fact pulling the coldest possible air (from the ground and recirculated air) into the evap coil, and driving air against its natural tendency to fall. air will fall naturally out of the evap coil.
    Quote Originally Posted by MikeHolm View Post
    The air movement as you state will be working against nature so I suspect the electrical draw might be a little bit higher but given the current draw I doubt it will be much. I haven't seen any heat pumps here that would be a downdraft because they are almost the units are offshoots of AC units.

    The ground temp at the house will be a few deg warmer than the ground 1m away from the house because it is not that well insulated. I had contemplated having the heat recovery exhaust exit the house under the unit or even within the box but it was technically difficult to do.

    If your air on and air off temps are only a few deg different and given the heat loss of the building at ground level (there is a full basement), I'm not sure that it will be an issue. 25 years ago we regularly had temps of -25 in the depths of the winter but the last few winters I can count very nights below -15C with most at -5 to -10. I use -15 as a goal which is why I was interested in the digital scrolls performance.
    Quote Originally Posted by MikeHolm View Post
    Mad, what do you think the performance change would be if the the fan was removed from the picture?
    Quote Originally Posted by mad fridgie View Post
    What yo have built is an excellent cond, (and this is what everybody does, even in this application)
    Here NZ the ground temp in the morning can be a good 6C below air temp,
    So for example if the fan where underneath, drawing air downwards and discharging along the ground, it is possible that the SST could be 6C higher (in the above case), that could increase duty by close to 15%.
    (off the top of my head)
    Quote Originally Posted by MikeHolm View Post
    Food for thought, as they say, I will have to look up norms but local temps (local meaning within a 1m or so) are very influenced by what is around them. Is the wasted heat through the wall of the house going to influence the air on temp when the coil is 600mm above the ground. I have never seen a study on this but I am sure it exists....somewhere
    Quote Originally Posted by Bigfreeze View Post
    I'd have to disagree with you there Mad. There would be almost no difference in the air temp a 300mm off the ground and that off air 1.3m off the ground. I would say almost none tbh. The disadvantage of downdraft in Mikes design is that it could encourage short cycling of air, which would be much worse than any potential gain.
    Quote Originally Posted by MikeHolm View Post
    Even tho it is 600mm off the ground and has free air on 3 sides? Maybe i am not getting the meaning of short cycling correct...
    Quote Originally Posted by mad fridgie View Post
    The comment is not particular to this evap, The air is drawn past the ground to enter the evap, hence must be colder, the air exiting is colder and more dense than the ambient so will fall to low level, encouraging short cycling.
    Many other factors do need to be considered exiting air velocity, free area in which it is to be mounted.
    Not to say that you would just mount the fan underneath.
    Quote Originally Posted by MikeHolm View Post
    Here is the next Evap I had in mind,
    Attachment 7921

    In the winter The solar panels are often unable to reach the temp needed to help the DHW tank but does contain enough heat to add to the evap. The question is, at what sustained temp would the coil be considered to be overheated? 40C? Assume 410A. Probably not enough info typical eh...
    Attached Images Attached Images
    Attached Files Attached Files
    If the World did not Suck, We would all fall off !

  29. #79
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Quote Originally Posted by MikeHolm View Post
    Morning CM. Are you doing this on a mobile while pissing away your employers time? LOL Or is it lunch time and you are in the pub.

    You are probably right about the historical stuff but I would think it would change by now. One benefit of the the lower pressure from the tank is less water consumption from showers. Toilets will fill slow tho. How do those toilets that work on 3 bar pressure to flush work in the UK?
    Hi Mike

    Mobile Internet (HSDPA) 2mb connection, pukka, can work and play at the same time

    R's chillerman
    If the World did not Suck, We would all fall off !

  30. #80
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Pulling a vacuum eh? bored?

    Still looking for thoughts on a combined coil? I don't know if there are any other combi coils there (boiler or other options)
    Last edited by MikeHolm; 13-10-2011 at 11:34 AM.

  31. #81
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi Mike

    when in defrost, I presume the fan is off ?

    would it be worth insulating the box the evap sits in ?

    also you are going for an angled evap this time, whats the benefit here ?

    R's chillerman

    (maintenance - get 8 hours for what takes me max 4)
    If the World did not Suck, We would all fall off !

  32. #82
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Yes, the fan is off for defrost, I may use hot solar heated water when available to defrost but we will see. The angled coil will aid in getting rid of liquid during defrost and it means I can mount the unit between the houses when there is only 1.8m of space, without pissing off the neighbour.

  33. #83
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi Mike

    many ventures all in one here, mate, certainly keep you busy and hopefully fat wallet when finalised

    another gremlin you have which warmer climates dont suffer is a drop in specific heat transfer

    if looking at -20*c .... glycol mix needs to be to -30*c ..... which I think is roughly 50/50

    cp of water is 4.18 where glycol is 2.36 ....... lowering efficiency of the already lower temps, heat transfer

    was thinking too that maybe during winter you often get clear skys and low sun as we do here, making your solar systems more available for work, but 'think' I recall you saying panels require +15*c to work well and winter sun is not as strong

    certainly got your work cut out here mate, finding the right balance of heat/energy/heat

    R's chillerman

    Argh ! A thought - what about magnification of the sun onto solar ?
    If the World did not Suck, We would all fall off !

  34. #84
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Nope, the normal hot water panels I use produce good heat in -15C -20C as long as it is sunny, which it often is in the winter but i may only get 30C from the panels and not 70-80C that i would like.

    Water/Glycol is 60/40 typical. There are additives that help the freeze/boil characteristics somewhat but you are right, transfer is not great. We are used to it in this business as there is not a lot of option except for system that drainback the water to an inside storage tank when not in use.

    All in all, solar does work well but financially, not unless you have some subsidy as you have.

  35. #85
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi Mike

    thats good, got my +/- round wrong way

    you can start fires with a magnifying glass, is this something that can be used to increase heat

    or is this something that is already part of a solar panel (built in)

    seems strange how some western countries subsidise some products and not others

    R's chillerman
    If the World did not Suck, We would all fall off !

  36. #86
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    I had a lot of t-stat and pump wiring to do before I started up the HP. Yesterday started it up for the first time with a floor heating load, got very high pressures for the first couple of minutes (tank was cold too???) then it settled down but pressure is getting near 400psi at 40C water temp and TXV is hunting a bit. I think I will put in a receiver tank if it will help the hunting issue. I really want something to keep the the pressure from passing the 400psi mark but I'm not sure what the best method should be...any ideas?

    superheat is running between 15-16F with a cold tank and 6F when it is near setpoint. DT on the water side in and out of the tank is about 4-5F
    Last edited by MikeHolm; 22-10-2011 at 10:04 PM.

  37. #87
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: My first self made EVAP

    Hi Mike

    if valve hunting, first confirm you have liquid feed by taking discharge pressure and convert to saturated temp, then check you have a lower temp on liquid line, if sure you have liquid feed then its just a case of getting the valve set up right

    you can increase discharge temp by increasing suction superheat, this will then give you a higher discharge temp at a lower pressure but on the flip side higher suction superheat will reduce mass and compressor work is increased to move the same mass ...

    what refrigerant are you using ? R410a for instance has high pressures but lower temp to pressure than other common refrigerants

    400psi is 27.2 bar which if R410a is fine

    R's chillerman
    If the World did not Suck, We would all fall off !

  38. #88
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Thanks CM, I will look at it again during the week.

  39. #89
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: My first self made EVAP

    Ignore the fact you have low discharge temps from cold. Its always the case when starting a heat pump. Only when the floors return water temp is 20C plus can you really zero in on whats happening in the fridge circuit.

    Starting the machine in cold weather you should actually help your discharge temps by slowing the pump speed until return is about 20C.

    What gas are you running. 407C i assume? 400psi is pretty high in that case. What are your inlet outlet temps across HX on water side?

    I would install a receiver. Just to give yourself a bit of leeway when it comes to refrigerant charge.

  40. #90
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    HI BF, it is a 410 machine but I will have to go back and take measurements tomorrow. Problem is that I am only running on stage one as i haven't put a 2nd stage switch on it yet and I am wondering what the best way would be to do that. Like I said above, I'm getting 10.5A @230VAC on stage one and this seems a bit high to me.

  41. #91
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: My first self made EVAP

    Quote Originally Posted by MikeHolm View Post
    HI BF, it is a 410 machine but I will have to go back and take measurements tomorrow. Problem is that I am only running on stage one as i haven't put a 2nd stage switch on it yet and I am wondering what the best way would be to do that. Like I said above, I'm getting 10.5A @230VAC on stage one and this seems a bit high to me.
    If its 410a then you're not a million miles out at 400psi. Your condensing temp should be about the same as your outlet temp give or take a degree or two. 400psi would be about 47C condensing.

    Dual stage? As in two compressors? I assume they're two 7kw units. If so, again you're not a million miles away assuming that that figure includes the fan motor and the fact you're running up towards 50C.

    Are you running a seperate coil for each compressor?

  42. #92
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    It is a ZPS two stage copeland,

    ZPS40K4e summary.pdf

    ZPS40K4E performance.pdf

    On full output it should pull 9.4A at 10C evaporating and 40 condensing and I will check what pressures we are running today, but last i checked, I was drawing more power than that and i hadn't reached a 40C tank temp yet.

  43. #93
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: My first self made EVAP

    Are you sure its evaporating at 10C. That would be high for this time of year. 0C would be more likely. According to the weather service its 11C in Toronto today, so no way its evaporating a 10C. 3C maybe.

  44. #94
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    I stand corrected, I meant that ambient was 10C. I haven't been down to the job today as they are finishing the wood stairs and I can't get in the basement. I will see tomorrow.

  45. #95
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    OK, the R410A HP seemed to be running well enough while the weather was a bit warmer. What bugged me most was the high current draw 15.5A when the data sheet says it should be 10.5A.

    I put on the gauges and I get suction 4.72Bar, -10C,
    discharge is 28 Bar, 48.3C
    Liquid from the buffer is 49C and out is 53C

    air on 9C and off is about 5C (comp stopped as it was going down and I was about to take pipe measurements on the evap) and the sun went down anyway.

    I was going over in the morning and when I got there the EVAP was a solid block of ice.

    I think it is overcharged but I have a feeling there is something else as well (perhaps condenser is too small). Any thoughts?

  46. #96
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: My first self made EVAP

    Quote Originally Posted by MikeHolm View Post
    OK, the R410A HP seemed to be running well enough while the weather was a bit warmer. What bugged me most was the high current draw 15.5A when the data sheet says it should be 10.5A.

    I put on the gauges and I get suction 4.72Bar, -10C,
    discharge is 28 Bar, 48.3C
    Liquid from the buffer is 49C and out is 53C

    air on 9C and off is about 5C (comp stopped as it was going down and I was about to take pipe measurements on the evap) and the sun went down anyway.

    I was going over in the morning and when I got there the EVAP was a solid block of ice.

    I think it is overcharged but I have a feeling there is something else as well (perhaps condenser is too small). Any thoughts?
    I'd definitely expect that kind of ampage draw on that size compressor with that much differential between low and high side. Try to keep the outlet temp down to 45C if possible. Running at high temps in heating mode will write off your compressor in a short space of time.

    Could well be overcharged as your condensing temp and water outlet temp should be within 1C of one another and right now they're 4-5C apart. Your subcooling should be close to your return temp too.

    Whats controling defrost and what type of defrost is it?

  47. #97
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    That's the problem, it is a York board with defrost built in. The manual gives no indication except that there are jumpers across pins depending on the size of unit. I assume that is for defrost time. There is a bonnet sensor, defrost sensor as well an ambient sensor.

    I assume it just triggers the reversing valve.

    It also mentions something called "Hot heat pump" but does not define what that means.

    Bugger....

    The above temp is the highest the unit gets to as my tank setpoint is 49C

  48. #98
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: My first self made EVAP

    I would say cond side is very good, suction does seem very low for that ambient and condensing pressure.
    (when dealing with temps and pressure which are very close, you may just find it is the accuracy of the instruments that you are using.)
    The amps are spot on, for those conditions.
    You need to work out why your suction is so low, at 9C and high SCT you should be well above freezing.
    Do you have sight glass in the liquid line?
    what is suction return temperature at the comp inlet.

  49. #99
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Suction return about 6" from the inlet was -10C.

    I am thinking of putting in a bigger pump to get a bit more out of the condenser. What do you think?

    As BF says try to narrow the gap some....I thought the condenser was a bit small
    Last edited by MikeHolm; 24-11-2011 at 12:43 AM.

  50. #100
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: My first self made EVAP

    Unfortunately there is no sight glass, my next concoction will have one