    Digital Scrolls



    OK, I know some of this has been covered before but I can't find it (CM always seems to be able to) but can anyone think of a reason NOT to use a digital scroll on a heat pump with an appropriately sized storage tank?

    Design info seems a bit lacking it seems as well.



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Digital Scrolls

    Hi Mike

    does this answer your question mate

    Quote Originally Posted by mad fridgie View Post
    We are taliking about water heating units that are used for static heating devices (rads and underfloor) so by pure nature is slow reacting, so quick response in temperature is just not required, I really can see a point for an inverter for this applicaqtion, at 10 starts an hours 6 mins off period on stastic heat exchanger will not change the feel of a home. (air to air systems with forced draft heating, inverter is required 100%)
    R's chillerman
    If the World did not Suck, We would all fall off !

  3. #3
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Digital Scrolls

    Yes, but the "reported advantage" by Copeland (for heating) of a digital scroll (not an inverter) is better low ambient performance over a single stage unit, and they state this advantage for ASHPs with a water storage!!!!!

  4. #4
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Digital Scrolls

    Argh I see

    running at part load in low ambients will decrease mass flow through the outdoor evap

    allowing more time for heat to be absorbed

    made up figures for example

    if at 0*c x amount of heat is added to refrigerant in evap at full load

    and at full load you have 1kg of refrigerant passing through evap per minute

    then at half load you have half kg of refrigerant passing through evap per minute

    you add more heat to that half kg increasing suction pressure/temp

    which in turn increases head pressure/temp

    if suction pressure/temp remains too low

    you will not gain enough head pressure/temp to heat the water to desired temp

    R's chillerman
    If the World did not Suck, We would all fall off !

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Digital Scrolls

    Why digital scroll? ZB will do the job just as good and at a lower price.
    Can you add HGB to keep the evaporator temp above 0C?

  6. #6
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Digital Scrolls

    Quote Originally Posted by chemi-cool View Post
    Why digital scroll? ZB will do the job just as good and at a lower price.
    Can you add HGB to keep the evaporator temp above 0C?
    Hi Chemi

    good point mate, hot gas bypass would do the same job nicely

    so still looks like Mike no need for digi mate

    just copeland sales pitch

    R's chillerman
    If the World did not Suck, We would all fall off !

  7. #7
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Digital Scrolls

    Just asking guys.....doesn't mean I believe them.

    Isn't HGB a bit of an energy waster though?....Ambient to be concerned with is -15C

    I think Mad would shoot me if i used HGB, may BigFreeze would too.

  8. #8
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Digital Scrolls

    Argh you got me now Mike

    if Mad would shoot you for using hgb, I'm not arguing

    he could be bigger than me and may be bumping into him soon

    and thinking about it

    you transfer energy to heat and then dump it back into low side with out using it to make hot water

    just to increase heat/mass hmmmm .... yeah does not sound economical when looking for efficient heat pump

    God Mr mike - you getting me thinking tonight and Mad will probaly turn up soon and say I got it all wrong

    R's chillerman
    If the World did not Suck, We would all fall off !

  9. #9
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Digital Scrolls

    He might tell me Chemi is spot on as well.....I must defer to my superiors on this and that is all you regulars...

    Come on Mad, chime in.....

  10. #10
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Digital Scrolls

    Mike

    Gary has also shown me recently along with DesA

    they all have an in depth understanding of heat/energy and efficient use

    which is all based around

    energy can niether be created or destroyed but transfered from one form to another

    as the heat has to be transfered from energy and not transfered from ambient

    when using hgb, it does appear your argument is justified with digital scrolls at -15

    they probaly all on holiday for a week or two and we be left wondering till then
    Last edited by chillerman2006; 09-10-2011 at 12:26 PM. Reason: created to transfered: Der
    If the World did not Suck, We would all fall off !

  11. #11
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Digital Scrolls

    we shall see if more of the jedi masters chime in.....I would like to have this discussion as i seldom hear anyone talk about them. Most of the talk is about inverters which I agree makes no sense in heating a big tank of water.

  12. #12
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,554
    Rep Power
    26

    Re: Digital Scrolls

    The simply question is "do you need close control of your water".

  13. #13
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Digital Scrolls

    Nope, you don't need close control of your water.....but the question is " given components of the same size, will the digital actually have a lower running cost then the ZB at -15C" or is it just that they believe the comp size can be reduced giving a lower running cost"
    Last edited by MikeHolm; 09-10-2011 at 12:09 PM.

  14. #14
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Digital Scrolls

    Wouldn't using a bigger evap on a static control unit give you the same result except for 100% of the time?
    An offloading digital scroll could be more than likely become undersized for the application when dropped to 75% load in winter running.

  15. #15
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Digital Scrolls

    Hi BigFreeze

    a larger evap would still give you the same heat transfer to a kg of refrigerant

    you need to either control mass flow (reduce it to increase transfered heat per kg)

    Or use another method such as hgb to increase mass/temp at compressor inlet at low ambients

    R's chillerman
    If the World did not Suck, We would all fall off !