Results 1 to 20 of 20
  1. #1
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Someone explain the answer to this please.



    Question. If the condensor fins are fouled or blocked, the HP increase but the LP also increases.
    In this case why does the LP increase.

    Answers 1. The Compressor draws in less vapour
    2. More liquid passes through the capillary
    3.Both suggestions are true
    4. both suggestions are false.

    WHICH IS CORRECT ANSWER
    thanks in advance
    Last edited by moondawn; 08-10-2011 at 05:47 PM. Reason: braindead



  2. #2
    Join Date
    Aug 2011
    Location
    england
    Posts
    29
    Rep Power
    0

    Re: Someone explain the answer to this please.

    l.p will be high as temperature hasnt been taken out of the hot gas in the condensor coil..

    expansion valve reduces valve pressure/temperature, but hot/gas liquid is at a high temperature/pressure than it should

  3. #3
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Someone explain the answer to this please.

    hi sweimaker cheers for reply which answer would you go with then?

  4. #4
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: Someone explain the answer to this please.

    also you have to remeber this is a chemical reaction/process taking place the suction and discharge pressures of any gas can only be so far apart so as the discharge rises so does the suction
    oh and to answer yr question both are wrong lol
    I can fix broke but I cant fix stupid :)

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Someone explain the answer to this please.

    Hi Moondawn

    a system has to balance and you have to match the heat absorbed in the evaporator to the heat rejected by the condensor

    with a bocked/dirty condensor the head pressure will rise due to increased suction pressure and the heat rejected is not enough to reduce the refrigerant to equal or below its liquid phase temperature for that pressure

    you then have a saturated vapour/liquid mix entering the evaporator instead of liquid

    a liquid can absorb more heat per area of evap due to its increased mass and any available subcooling

    lets just make up some figures for example

    as a liquid the evap holds a kg of refrigerant and x amount of heat is transfered into the refrigerant by evaporator

    as a saturated vapour/liquid mix you have less mass for instance 3/4 of a kg

    but you are still transfering x amount of heat into the refrigerant by the evaporator

    x amount of heat added to 1 kg of refrigerant = 4bar
    x amount of heat added to 3/4 kg of refrigerant = 6bar

    R's chillerman
    If the World did not Suck, We would all fall off !

  6. #6
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Someone explain the answer to this please.

    The answer is 4.

    Compressor can't pull less vapour as there is only vapour being drawn in the form of superheated and not sub cooled refrigerant.

    There won't be a full column of liquid in the liquid line to be passed through the cap or XV to be flashed into a gas.
    Training may be finished but experience is never complete.

  7. #7
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Someone explain the answer to this please.

    Quote Originally Posted by chilliwilly View Post
    The answer is 4.

    .
    Argh chillywilly

    thats cheating mate, i just give him all the facts so as 'Mad' does - gives me enough info for me to learn

    rather than the answer

    R's chillerman
    If the World did not Suck, We would all fall off !

  8. #8
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Someone explain the answer to this please.

    I'm sorry beegli beegli I'm sorry.

    I didn't want to give a too longer explanaition as there was already enough to chew on
    Training may be finished but experience is never complete.

  9. #9
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Someone explain the answer to this please.

    Quote Originally Posted by chilliwilly View Post
    I'm sorry beegli beegli I'm sorry.

    I didn't want to give a too longer explanaition as there was already enough to chew on
    Haha ok mate

    think there is plenty to chew on now you mention it

    R's chillerman
    If the World did not Suck, We would all fall off !

  10. #10
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Someone explain the answer to this please.

    Right or wrong I think its 1.
    The compressor will become less efficient as the pressure differential across it increases.

    The piston has to go down further before gas enters cylinder, due to top dead centre clearance volume.

    As far as more or less refrigerant passes through capilliary, I'm thinking hard to say as probably inefficient
    poor quality liquid/gas.

  11. #11
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Someone explain the answer to this please.

    Hi Lee,

    I like these questions. Most of us know the symptons but getting inside the pipework and imagining what is happening and why sorts the men from the boys. That said, I'm still definatly a boy in that respect!

    I reckon as HP increses by a larger proportion than LP then more vapour is drawn in. Also the vapour is more superheated.
    There would be less liquid in the cap tube as less liquid available from the condensor. Also it is at a higher saturated temp so as it cools along the tube it flashes off earlier

    Therefore answer 4 correct.

    Not quite sure of my theory about the vapour but seems right through my 'boys' eyes. Needs a 'man' to confirm!

    Cheers,
    Andy,
    Health and safety first..........unless I'm in a hurry.

  12. #12
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Someone explain the answer to this please.

    Hi Tayters

    I am still only one of the boys but all correct to me

    the system is a constant wheel that has to balance

    suction pressure/temp increase, then increases discharge pressure/temp

    higher pressure/temp at a blocked coil can not reject enough heat to reduce liquid phase

    mixed vapour in evap has increased pressure/temp per kg of refrigerant

    the compressor now shifts a lower mass due to increased superheat and superheats each kg of refrigerant more

    and the cycle continues until the point of equilibrium is reached

    eg: R407c abient 25*c & 12*c evap on temp = 19bar.g/4.4bar.g

    now becomes with blocked coil 23bar.g/6bar.g

    and thats without considering, fractionating with R407c before one of my peers start

    saying I have missed a bit

    R's chillerman
    If the World did not Suck, We would all fall off !

  13. #13
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Someone explain the answer to this please.

    hi all, thanks for your replies the question is off a program called kotza and i was going through the cycle as best as i could (limited knowledge although) and could not understand why kotza was giving the answer as C.
    It tells me the anser is both suggestions are true.

    i could not understand how "more liquid passes through the capillary" as it would be flash gas more than liquid.

    i to think the answer is D and i think that the answer on Kotza is wrong. its good to see how others have worked the answer out as that also teaches my way of thinking.
    as tayters says its hard to see whats going on inside the pipes and these questions do challenge.

    cheers lee

  14. #14
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Someone explain the answer to this please.

    Hi moondawn

    I have 'kotza' mate and I agree with you

    Kotza has some gremlins/false answers

    less vapour at compressor inlet by higher superheat

    mass flow through the cap is dependant on state of refrigerent

    velocity will increase due to higher pressure

    but liquid can only increase 'if' the sate of refrigerant is still liquid

    and not a vapour/liquid mix

    R's chillerman
    Last edited by chillerman2006; 10-10-2011 at 10:16 AM.
    If the World did not Suck, We would all fall off !

  15. #15
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Someone explain the answer to this please.

    Draw the circuit on a PH chart and you will notice that the quality of the refrigerant entering the evaporator reduces as the discharge pressure goes up, (greater 2 phase) which results in the evaporator not being full of liquid, and this increases suction superheat.

    With a high temperature suction gas entering the compressor, you then add the heat of compression to it, resulting in a higher than design discharge temperature.

    Don't forget that the first 3K of superheat is useful but any additional superheat is un-useful (wasted energy)

  16. #16
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Someone explain the answer to this please.

    well thanks all will continue to use it and any more questions i aint sure abouts will post and discuss.

    cheers

  17. #17
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Someone explain the answer to this please.

    Hi, moondawn

    Quote Originally Posted by moondawn View Post
    Question. If the condensor fins are fouled or blocked, the HP increase but the LP also increases.
    In this case why does the LP increase.

    Answers 1. The Compressor draws in less vapour
    2. More liquid passes through the capillary
    3.Both suggestions are true
    4. both suggestions are false.

    WHICH IS CORRECT ANSWER
    thanks in advance
    3. Both suggestions are true ... why...

    Drawing this cycle on the Mollier chart .... having condensing pressure above normal (both for water and air cooled condensers) due to...

    a) air or noncondensable gases in system
    b) partially blocked or dirty condenser
    c) high ambient temperature
    d) high temperature cooling water
    e) insufficient cooling water
    f) high ambient air temperature
    g) insufficient air flow

    result is ....

    1) Condensing pressure - increase
    2) Evaporating pressure - increase greatly in case of capillary tube, but superheat decrease, in case with expansion valve evaporating pressure increase a little, but SH remains constant

    3) Compression ratio - increase
    4) Specific volume of suction vapor little decrease
    both are giving reduced weight of circulated refrigerant i.e. cooling capacity decrease

    Refrigerating effect decrease....
    C.O.P decrease and due to higher condensing pressure running current increase..



    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  18. #18
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Someone explain the answer to this please.

    Quote Originally Posted by Josip View Post
    result is ....

    1) Condensing pressure - increase
    2) Evaporating pressure - in case with expansion valve evaporating pressure increase a little, but SH remains constant

    Hi Josip

    I cant understand how superheat can remain constant

    If the mass in evap is decreased (from liquid to mixed vapour) and heat transfer remains constant

    Then pressure and superheat have to go up surely ???

    As was the case with a unit I worked on just the other day

    6bar.g suction and 18*c superheat with blocked coil

    Once coil cleaned 4.4bar.g suction and 11*c superheat

    With the same water outlet temp

    (have also edited post #14 to be more accurate)

    Regards chillerman
    Last edited by chillerman2006; 10-10-2011 at 10:18 AM.
    If the World did not Suck, We would all fall off !

  19. #19
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Someone explain the answer to this please.

    Well, this is a tricky one.
    Ok if both 1 and 2 are right, then the program is wrong, if you increase the liquid mass flow through the expansion device, then you must increase the mass flow through the compressor (this not about net refrigeration effect)
    How ever your liquid/vapor % leaving the expansion valve will increase (more vapour) this then leaves less liquid to absorb load. Your heat ex-changer will reach equilibrium, so if you can not absorb the design amount of energy, then temp difference across the heat exchanger will reduce lifting the suction pressure. Depending upon the suction superheat, your actual compressor inlet mass flow could increase.
    Then we have to consider the volumentric efficiency of the compressor, if it is a recip, then as compression ratio increases, the volumetric efficiency decrease (less actual mass flow through the compressor)
    So really no a straight forward question.

  20. #20
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Someone explain the answer to this please.

    well thats me baffled again :-)
    mad fridgie which one do you think is the answer or you thinking the question is not clear enough?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •