Thread: trane chiller
-
06-10-2011, 07:16 PM #1
trane chiller
have a trane chiller with faulty crank case heaters that are 415 volt can only seem to get 230 volt from supliers any one no who supplies them other than trane
-
06-10-2011, 09:59 PM #2
Re: trane chiller
415v to 240v tranny?
Mostly found in Oxfordshire, UK :)
-
06-10-2011, 11:02 PM #3
Re: trane chiller
L1+N can often give the correct voltage..
-
07-10-2011, 12:09 AM #4
-
24-11-2011, 05:43 AM #5
Re: trane chiller
As far as I know all Trane gear bigger than splits is 3 phase only, no Neutral.
-
24-11-2011, 07:02 AM #6
Re: trane chiller
would make sense, and would probably explain why they used a 415v heater in the first place
i had a faulty time clock that controlled a filter cleaning cycle for a cooling tower system, that was 415v because it only have 3 phases run to it, i searched and searched and could not find a 415v time clock anywhere to replace it, i had to install a transformer and a 240v one, running a neutral was out of the question.
i have seen quite a few 415v crankcase heaters around though, so i would have thought they wouldnt be that hard to find, but iv never tried to buy one either.... so good luck!