Page 2 of 2 FirstFirst 12
Results 51 to 98 of 98
  1. #51
    Apr 2006
    55
    1,908
    30
    Re: Strage Pipework Configuration
    Quote Originally Posted by marc5180 View Post
    Chillerman,
    A suction line accumulator should be sufficiently sized to hold the entire charge of the system.
    Hi Marc
    should it ?
    you got me, when it comes to designing and component choice
    but does seem excessive to me mate
    If correct ...would you say this units accumalator is big enough ?
    R;s chillerman
    If the World did not Suck, We would all fall off !
  2. #52
    Oct 2007
    manchester
    5,639
    45
    http://www.stara.co.kr/parker_catalo...og/40-10-7.pdf
    Quote Originally Posted by chillerman2006 View Post
    Hi Marc
    should it ?
    R;s chillerman
  3. #53
    Mar 2006
    Lancashire
    1,859
    28
    On a heat pump air conditioner the defrost is nearly (if not always) carried out by the hot gas method, i.e. the reversing valve is energised to flood the outdoor coil with "hot gas". As this coil will be 90% full of liquid it will be pushed down the suction line and has to be collected by the accumulator to protect the compressor - hence the accumulator must be able to hold the entire charge.
    Marc
  4. #54
    Oct 2007
    manchester
    5,639
    45
    Systems with a thermostatic expansion valve (TEV), the
    accumulator holding capacity should be approximately 50%
    of the system charge.
    from parker
  5. #55
    Apr 2006
    55
    1,908
    30
    Argh, I see cheers
    So does the hidden accumalator have that capacity, mate
    (marc's thinking ''I started this thread for answers not starting up a training school )
    R's chillerman
  6. #56
    Jun 2009
    Lusk , Dublin
    1,115
    I could be wrong but....I always thought a suction accumulator should be sized for 50% of refrigerant charge and a liquid receiver was 100% of charge.
    Stu
    Tool's ? check ! Condom's ? check !
  7. #57
    Oct 2007
    manchester
    5,639
    45
    http://www.refrigerationbasics.com/1...eat_pumps1.htm
    in defrost mode the liq still travels through the 4 way valve and creates cooling in the evap thats why ur indoor fan slows down whilst in defrost mode
  8. #58
    Oct 2007
    manchester
    5,639
    45
    stu u are wrong,but u are correct! brownie point for u!!
  9. #59
    Apr 2006
    55
    1,908
    30
    Quote Originally Posted by install monkey View Post
    Thanks Install
    have kept a copy of that, a useful bit of info Cheers
    Quote Originally Posted by stufus View Post
    Stu
    Hi Stu
    as per 'Installs' link you would be correct mate on refrigeration systems
    But it does not state clearly for systems with reverse cycle or for heat pumps
    And 'Marc s' comment makes sense, would you agree ?
    R's chillerman
  10. #60
    Mar 2006
    Lancashire
    1,859
    28
    Haha far from it CM,
    Install, i've read what Parker say that and by the size of the accumulator that is fitted then i would say they have probably used one that is 30-50% of the entire charge but what happens if a componet fails.
    The size of an accumulator is based upon the size of the error, and the likelihood of the error you think can occur
    Marc
  11. #61
    Mar 2006
    Lancashire
    1,859
    28
    Marc
  12. #62
    Apr 2006
    55
    1,908
    30
    irrelevant
  13. #63
    Oct 2007
    manchester
    5,639
    45
    you dont have the power to give fractions yet! haha-nike 123 give me a pic of a pint of guiness and a bird wrapped in duct tape- that wasnt frowned upon!!
  14. #64
    Mar 2006
    Lancashire
    1,859
    28
    Liquid travels through a 4 way valve?? Where?
    On a 4 way rv you have discharge and suction vapour pressures not liquid.
    Marc
  15. #65
    Oct 2007
    manchester
    5,639
    45
    my bad
  16. #66
    Jun 2009
    Lusk , Dublin
    1,115
    Suction accumulators are also system specific IE you should not use a standard SA on a heatpump system due to the orifice size being to big and allowing liquid slugging to the compressor especially in heating.
    http://www.henrytech.com/Tips/HT-TT14.pdf
    C
    heers
    Stu
  17. #67
    Apr 2006
    55
    1,908
    30
    irrelevant
  18. #68
    3,853
    I've heard half system charge as a rule of thumb for accumilator sizing.
    Jon
  19. #69
    Oct 2007
    manchester
    5,639
    45
    chillerman
  20. #70
    ireland
    1,451
    41
    Thanks Marc
    You've had one electrical fault and the other sounds like liquid flood back, i'm with install on this,these dx units must be held off in ambients below 16c, i know theres plenty of heat at the minute but i doubt that was the case before this week? If the units are required to run in lower ambients you've a sizing issue. I can't imagine a heat pump with no accumulator, so look at control strategy and airflow first, see Gary we do listen!!
    al
  21. #71
    Oct 2007
    manchester
    5,639
    45
    hmmm-post missed with all the chat over accumulators-other points to consider-
    no crankcase heater on the pot, system is within the airflow so exposed to 10-40deg ambient, no jacket on the compressor, as u say no suction accumulator or evap press reg, as with air handling units normally 100% fresh air then sticking a cooling coil in there there is not a constant load so theyve done well sticking an electronic expansion valve-at least it will be more responsive, also them check vavles will need checking to ensure theyre not passing as with the 4 way valve as its too easy to chuck a pot in and watch it destroy itself, also i would look at the control strategy, comp restart delay, setpoint differential it should have a free cooling setpoint that usually is set around 16 deg which will stop the mechanical cooling and rely on fresh air.
    are the v belts ok,if fitted,panel filters blocked as they normally last 3mth also check alarm history, is there a lp swith on it or transducer, may be sartup of the compressor causing pipework to flex and the lp being auto reset??
    are the fans inverter driven whats the minimum speed or is it controlled of duct pressure?
    i could nip up to site as its in my hood!!haha
  22. #72
    Apr 2006
    55
    1,908
    30
    Install
    Just because no-one replied to your post the last time round
    R's chillerman
  23. #73
    Oct 2007
    manchester
    5,639
    45
    my post co
    Last edited by install monkey; 02-10-2011 at 08:30 PM. Reason: cut out the adverts!!
  24. #74
    Dec 2010
    Toronto, Canada
    1,454
    irrelevant
  25. #75
    Oct 2007
    manchester
    5,639
    45
    molson per
  26. #76
    Dec 2010
    Toronto, Canada
    1,454
    irrelevant
  27. #77
    Dec 2010
    Toronto, Canada
    1,454
    irrevelant
  28. #78
    Apr 2006
    55
    1,908
    30
    irrelevant
  29. #79
    Oct 2007
    manchester
    5,639
    45
    is that ur
  30. #80
    Dec 2010
    Toronto, Canada
    1,454
    irrelevant
  31. #81
    Apr 2006
    55
    1,908
    30
    irrelevant
  32. #82
    Apr 2006
    55
    1,908
    30
    irrelevant
  33. #83
    Mar 2006
    Lancashire
    1,859
    28
    11 posts spamming.....
    Marc
  34. #84
    Mar 2006
    Lancashire
    1,859
    28
    Quote Originally Posted by al View Post
    Thanks Marc
    al
    These units are only designed to temper the air and so run all year round using a recouperator and a mixture of fresh air and return air
    When the outdoor temp gets to cold they use full return recirculation with minimum fresh air.
    The minimum air onto the coil is 18DegC.
    Marc
  35. #85
    ireland
    1,451
    41
    Check the accumulators for size and correct piping (inlet/outlet), could be worth getting a thermal camera for a day to see what's going on?
    al
  36. #86
    Mar 2006
    Lancashire
    1,859
    28
    Not all compressors have visible crankcases though do they? Many of them have a voltage going through the windings to heat the compressor a few degrees.
    Minimum air onto these coils/compressors is 18DegC
    Compressor restart delay is 6 min. These have a recouperator that mixes fresh air and return air and if the temp is still too high/low then the compressors will be brought on. The setpoint for the building is 21/22 degress C so the compressors don't need to be on often....supposedly.
    Filter/belts ok
    Yes theres an LP switch on it, looked at alarm history and found only the 1 LP fault.
    Compressor flex and reset the LP alarm ?? Can that happen??
    Yes the fans are inverter driven and have been commissioned to run at 50hz
    Lol, Nip up to the site to do what?
    Marc
  37. #87
    Mar 2006
    Lancashire
    1,859
    28
    Thermal camera? To check what?
    Marc
  38. #88
    ireland
    1,451
    41
    check the accumulator for a start, also check your 4 way valve and NRV's.
    In fairness this is either the site completely screwing up the units or they have been misapplied or specced?
    al
  39. #89
    Aug 2009
    New Zealand
    2,554
    26
    Copeland say that the scroll is compliant, it can handle liquid flood back ( a slug of liquid), say after defrost, in this case it is the position of the EEV temp and pressure sensor causing prolonged oil dilution,
    Accumulator size, without knowing all the data I would just go for one which is has the same size pipe as the comp inlet. You could even look a suction/liquid line heat exchanger (between the EEV sensor and the comp)
  40. #90
    ireland
    1,451
    41
    MF, i've found scrolls less tolerant of flood back, more inclined to wash oil out and not return it, accumulator would be essential as you say.
    al
  41. #91
    Mar 2006
    Lancashire
    1,859
    28
    Thats a good idea al, I may suggest that.
    When i find out more i'll update the thread, thanks for your input. Much appreciated
    Marc
  42. #92
    Apr 2006
    55
    1,908
    30
    Gents
    just a quick thought as bed time for me
    dont certain copeland scroll models have built in accumalators that allows them to take full liquid and boils it off by compressor heat ???
    R's chillerman
  43. #93
    Aug 2009
    New Zealand
    2,554
    26
    al
    Before I starting producing my units, I did considerable testing on the scrolls, and found that under certain circumstances liquid return was a problem, so even though the tech data says i do not need a accumulator, I do fit one, in my mind it is cheap protection.
    CM; copeland scrolls do not have a built in Acc, Maneurope recip comps do. (twin shell)
  44. #94
    Apr 2006
    55
    1,908
    30
    Quote Originally Posted by mad fridgie View Post
    Thanks Mad
    Thought I was going 'mad' when the thought appeared in me head, argh so its maneuropes (recips) Cheers for correction
    Also picked up a site with a right mickey mouse abortion of a setup (1st visit today) with 4 copeland scrolls, it looks a right b*tch to change 3 of the four compressors
    Mad, in your eyes, whats the perfect suction superheat for copeland scrolls (as I need them to purr for ever)
    R's chillerman
  45. #95
    Oct 2008
    newbury
    1,444
    37
    Is anyone doing a failure test on the failed compressors
  46. #96
    Oct 2007
    manchester
    5,639
    45
    Can Copeland Scroll compressors handle liquid?
    ANSWER: Scrolls handle liquid better than most other compressor types, but still can require additional accessories for optimal protection. Those accessories include: Accumulators are recommended for systems with large refrigerant charge or those that allow for uncontrolled refrigerant floodback. Crankcase heaters are required for three-phase systems with large refrigerant charge and in/outdoor applications.
    ref copelands website
  47. #97
    Mar 2006
    Lancashire
    1,859
    28
    Just to update the thread. The system was found to have a leak on the equalising line. The manufacturers went back to site to repair.